    Hot water not coming on when requested

    Hello guys, I have had my system installed for nearly 2 years now and for most of it it works flawlessly. I even have it integrated in to Alexa :-) :-)
    Since day one though I have always been getting a boiler actuator relay fault. As the heating and hot water were both working as normal I just used to cancel the message. After doing a bit of research I found that this could be caused by double bonding. So on the controller I removed the stored hot water or should I say disabled and on the heating control I selected none. I then went on and selected enabled for the sored hot water and went through the bonding process with the cs92. I then get the success and it asks me what sort of system, I select 2 or 3 valve and it asks me to bond again which I am presuming they mean the BDR91 which I go through the 15 sec and 5 sec routing I get the success again and it asks me to bond the heating actuator which again I am presuming they mean the other BDR91 I have connected to my heating. All seemed to go through without any problem. However the boiler will not come on when I request the hot water on and although the heating will come on and go off the green light on the BDR91 is staying on even though the boiler is off. Have any of you far more knowledgeable chaps than me got any ideas as to where I have gone wrong?
    Thanks
    Will
  • willdonal
    Automated Home Sr Member
    • Oct 2017
    • 58

    #2
    Update, after an hour the green light went off :-) :-)

    Comment

    • willdonal
      Automated Home Sr Member
      • Oct 2017
      • 58

      #3
      OK, in case any other member has a problem like mine I have managed to fix it by doing a complete factory reset and rebonding 14 HR92, 2 x BDR91 and the cs92. Had to do it twice as the first time the heating was coming on when the hot water was switched on. Now fingers crossed all seems good to go. I'll be an expert at this malarkey before long :-) :-)

      Comment

      • willdonal
        Automated Home Sr Member
        • Oct 2017
        • 58

        #4
        Spoke to soon, Heating coming on, or should I say the heating BDR is turning on when the hot water BDR comes on :-( :-(

        Comment

        • G4RHL
          Automated Home Legend
          • Jan 2015
          • 1580

          #5
          Originally posted by willdonal View Post
          Spoke to soon, Heating coming on, or should I say the heating BDR is turning on when the hot water BDR comes on :-( :-(
          When setting up there is a sequence to follow which I think I remember correctly is to set up the hot water function first and then configure zones. I had issues when I first installed Evohome 4.5 years ago but doing a fresh installation and following guidance the Evohome Shop gave in these pages all worked.

          The other possibility for your problem may be the proximity of the relays and devices to each other. A minimum of 30cms separation is recommended.

          Comment

          • dty
            Automated Home Ninja
            • Aug 2016
            • 489

            #6
            It sounds like your hot water BDR is double-bound. Did you clear the bindings from all devices (BDRs, CS92, HR92s) when you reinstalled?

            Comment

            • willdonal
              Automated Home Sr Member
              • Oct 2017
              • 58

              #7
              Originally posted by G4RHL View Post
              When setting up there is a sequence to follow which I think I remember correctly is to set up the hot water function first and then configure zones. I had issues when I first installed Evohome 4.5 years ago but doing a fresh installation and following guidance the Evohome Shop gave in these pages all worked.

              The other possibility for your problem may be the proximity of the relays and devices to each other. A minimum of 30cms separation is recommended.
              Thanks for the reply. Originally the BDR's were side by side as the installer hadn't read the installation procedure properly. I then got an official Honeywell installer to come down and sort it out. the first thing he did was to move the 2 BDR's so there was a 300mm gap between them and any other pipes etc. I did set the water side up first but got a bit confused when after binding the cs92 it then asks me what type of system I have, I then have to bind the Hot water BDR but it then asks me to bond the heating BDR. Then when I go back to the setting I then select the boiler control and select wireless relay box and it asks me to bond it again. So I'm presuming this is where the double bonding comes in. I have played around with different selections and at the moment I have got it back to square one where I am getting a boiler relay fault coming up but at least the heating is not coming on with the water.

              Comment

              • willdonal
                Automated Home Sr Member
                • Oct 2017
                • 58

                #8
                Originally posted by dty View Post
                It sounds like your hot water BDR is double-bound. Did you clear the bindings from all devices (BDRs, CS92, HR92s) when you reinstalled?
                Hi, yes I did the old press for 15 seconds till it flashed quickly then 5 seconds to make it flash slowly, then did the bonding

                Comment

                • dty
                  Automated Home Ninja
                  • Aug 2016
                  • 489

                  #9
                  Originally posted by willdonal View Post
                  Thanks for the reply. Originally the BDR's were side by side as the installer hadn't read the installation procedure properly. I then got an official Honeywell installer to come down and sort it out. the first thing he did was to move the 2 BDR's so there was a 300mm gap between them and any other pipes etc. I did set the water side up first but got a bit confused when after binding the cs92 it then asks me what type of system I have, I then have to bind the Hot water BDR but it then asks me to bond the heating BDR. Then when I go back to the setting I then select the boiler control and select wireless relay box and it asks me to bond it again. So I'm presuming this is where the double bonding comes in. I have played around with different selections and at the moment I have got it back to square one where I am getting a boiler relay fault coming up but at least the heating is not coming on with the water.
                  If you don't have a BDR controlling the boiler, you probably shouldn't bind a BDR in the boiler control section!

                  Comment

                  • willdonal
                    Automated Home Sr Member
                    • Oct 2017
                    • 58

                    #10
                    Originally posted by dty View Post
                    If you don't have a BDR controlling the boiler, you probably shouldn't bind a BDR in the boiler control section!
                    Hi, thanks for the reply. I have 1 BDR to control the water, eg to turn the boiler on to heat the water and another BDR to turn the boiler on for the heating. Would I not require the 2 BDR's to control the separate systems?
                    Cheers
                    Will

                    Comment

                    • dty
                      Automated Home Ninja
                      • Aug 2016
                      • 489

                      #11
                      I can't be certain from your description, but it sounds to me like you have 1 BDR controlling the hot water valve to allow hot water into the hot water cylinder, and 1 BDR controlling the central heating valve to let hot water into the radiators. The valves control the boiler via the orange wires. Unless you have a BDR directly connected to your boiler (which is an option, but most people don't have), then don't tell Evohome to control your boiler - let the switched lives (orange wires) from the valves do that.

                      Comment

                      • paulockenden
                        Automated Home Legend
                        • Apr 2015
                        • 1719

                        #12
                        Exactly what @dty has said. This seems to be a really common error when installing Evohome with S-Plan systems. Even my "professional" installer did this.

                        P.

                        Comment

                        • willdonal
                          Automated Home Sr Member
                          • Oct 2017
                          • 58

                          #13
                          Originally posted by dty View Post
                          I can't be certain from your description, but it sounds to me like you have 1 BDR controlling the hot water valve to allow hot water into the hot water cylinder, and 1 BDR controlling the central heating valve to let hot water into the radiators. The valves control the boiler via the orange wires. Unless you have a BDR directly connected to your boiler (which is an option, but most people don't have), then don't tell Evohome to control your boiler - let the switched lives (orange wires) from the valves do that.
                          Thanks dty, Yes that is how my system is set up, 1 BDR for the hot water and one BDR for the heating with a hot water cs92 connected to the hot water tank. I will try setting it up again without the boiler part selected. Thanks for your help
                          Will

                          Comment

                          • willdonal
                            Automated Home Sr Member
                            • Oct 2017
                            • 58

                            #14
                            Originally posted by paulockenden View Post
                            Exactly what @dty has said. This seems to be a really common error when installing Evohome with S-Plan systems. Even my "professional" installer did this.

                            P.
                            Thanks Paul, I will try what dty said and see how we go
                            Will

                            Comment

                            • willdonal
                              Automated Home Sr Member
                              • Oct 2017
                              • 58

                              #15
                              Hi all, thought I had sussed it. Got no fault reported on the controller and heating and water was working as it should, or so I thought. The hot water is set to come on at 5pm and Ive just gone in to the garage and both the BDR's are lit again :-( :-( I skipped the boiler part when setting up the water but then went in to the settings again and selected boiler control. Selected the wireless box option and bonded it to the controller. I am going to set it up again and leave this option as none but I suspect by not selecting this then the heating will not work at all. Pooh Pooh and more Pooh :-( :-(