    Default Intergas Diagnostic Software S1-S5 temperatures

    Does anyone know what the S1-S5 temperatures logged in IDS are?

    S1 Flow sensor?
    S2 Return sensor?
    S3 DHW sensor?
    S4 ???
    S5 Outside temperature sensor?


    Thanks!

  2. #2
    Automated Home Legend paulockenden's Avatar
    Join Date
    Apr 2015
    Location
    South Coast
    Posts
    1,602

    Default

    There's an option sensor that you can connect to the DHW incoming (I use it as I have a pre-heat tank). Perhaps it's that?

    Difficult to know because Intergas are a bit crap at exposing these readings. There's no S2 available via OpenTherm, for example.

  3. #3
    Automated Home Jr Member
    Join Date
    Sep 2018
    Posts
    12

    Default

    Quote Originally Posted by paulockenden View Post
    There's an option sensor that you can connect to the DHW incoming (I use it as I have a pre-heat tank). Perhaps it's that?

    Difficult to know because Intergas are a bit crap at exposing these readings. There's no S2 available via OpenTherm, for example.
    Paul, are my guesses correct? Do you know?

  4. #4
    Automated Home Guru
    Join Date
    Feb 2016
    Posts
    230

    Default

    I think Paul's correct about S4. Google came up with this Dutch manual which labels S4 as the 'Cold water sensor' i.e. flow-in from a pre-heater (Solar Water Heater in this example).
    https://www.intergas-verwarming.nl/w...E-88557803.pdf

    This manual gives these definitions:

    S1 Flow temperature sensor
    S2 Return temperature sensor
    S3 DHW temperature sensor
    S4 Cold water temperature sensor
    S5 Flow sensor DHW

    Do these seem to make sense?

  5. #5
    Automated Home Jr Member
    Join Date
    Sep 2018
    Posts
    12

    Default

    Quote Originally Posted by DanD View Post
    I think Paul's correct about S4. Google came up with this Dutch manual which labels S4 as the 'Cold water sensor' i.e. flow-in from a pre-heater (Solar Water Heater in this example).
    https://www.intergas-verwarming.nl/w...E-88557803.pdf

    This manual gives these definitions:

    S1 Flow temperature sensor
    S2 Return temperature sensor
    S3 DHW temperature sensor
    S4 Cold water temperature sensor
    S5 Flow sensor DHW

    Do these seem to make sense?
    I currently see:

    S1 95.2
    S2 46.7
    S3 - (will try priority DHW later to see whether this returns DHW temperature)
    S4 53.2
    S5 -2.3

    Temp Flow 63.7

    I have an Intergas HRE4 40 SB.

    S5 looks to me to be outside temperature (I have a sensor connected).
    S4 varies a lot more than S2, so I was thinking that was maybe Temp Return?

  6. #6
    Automated Home Jr Member
    Join Date
    Sep 2018
    Posts
    12

    Default

    I confirmed S4 is the DHW cylinder temperature reading. Also indicated I had an issue with my Priority DHW setup.

    One of the DHW BDR9s that was supposed to be normally closed and connected in parallel to the cylinder sensor was not connected!

    All working now (with boiler set to DHW Comfort ECO) see a DHW flow temp of 80C when there is a DHW demand rather than CH setting of 65C (OpenTherm).