    Default Evohome set an override by itself - linked to comms fault?

    Noticed a comms fault on the panel this morning, for that zone it is showing an override of 20C set (normally 12 is the programmed value). Wasn't sure if this was a a reporting glitch so went to the room in question.

    The room has two HR92s and a dedicated thermostat unit. One HR92 was completely dead, the other and the thermostat were running fine.

    The radiator with the still-working HR92 was indeed on full blast. I actually have no idea how long this has been the case, if it's been heating an unused room long-term that's not good!

    Can anyone shed any light on this? The fact the main controller reports the override makes me think it's not a rogue HR92?

  2. #2
    Automated Home Legend paulockenden's Avatar
    Join Date
    Apr 2015
    Location
    South Coast
    Posts
    1,719

    Default

    Perhaps the dead HR92 died when the room was last heating up, and just after sending a 100% heat demand?

  3. #3
    Automated Home Guru
    Join Date
    May 2017
    Posts
    148

    Default

    If you have multiple HR92s in a zone you set one as master, but if you also have a thermostat is this still the case, or does the controller talk to the thermostat? If the latter, it should be controlling the still-alive HR92 at the last program?

    Doesn't explain the override on the controller either.

    Also - I never thought of this buy can you get email notifications of battery/actuator issues like you can service failure/restoration?

  4. #4
    Automated Home Jr Member
    Join Date
    Mar 2019
    Posts
    16

    Default

    The override showing on the main controller when nobody set an override, is a well known problem. I get it fairly regularly on a system with 11 HR92s.

    If the central unit sends a temp setting to the HR92 but the HR92 doesnt get it -then when occasionaly the HR92s send their current temp setting to the central controller, the controller interprets the difference as a manual override and sets it accordingly.
    - this daft behaviour is because unbelievably Honeywell implemented a comms protocol without units acknowledging each other.

    - this normally sorts itself out when the central controller sends the next set point to the HR92 (assuming it gets it) so unlikely its been heating the room for a long time.