Thread: Evohome: living room getting warmer when warming other room!!??

Threaded View

Previous Post Previous Post   Next Post Next Post
  1. #1
    Automated Home Lurker
    Join Date
    Dec 2019
    Posts
    2

    Default Evohome: living room getting warmer when warming other room!!??

    I don't know what to do anymore...

    The Evohome system seems to be stupid, not able to control logically.

    Situation:
    Living room: SET: 19C, MEASURED: 19.5 VALVE % on touch display: 18%

    So I want to heat up my Study: the system is heating up the boiler.
    So far so good...


    BUT NOW the living room is also getting hotter because the HR92 does not close!
    touch display reading of living room valve remains on 18% (on HR92 valve position is 42%)

    Living room is heating up, 1 degree above SET temp of 19C and valve is not closing yet

    What is going on???

    I think I have had it with this system, I can return it until jan 31 unless someone has some suggestion??

    I do hope on some help, missing things I did not though of
    Thanks!


    DOMOTICZ SCREEN DUMP:

    here you see overshoot in STUDY when living room is heating AND overshoot in LIVING ROOM when study is heating up
    Last edited by wwjd1924; 22nd December 2019 at 01:36 PM. Reason: adding picture