Originally Posted by
rs1987
Yes, I turned Evohome back to its normal set point. It only anti-cycles, and infrequently, when the rest of the zones are up to temperature and there is only one rad open. It's a big improvement.
You're correct that the rads are undersized in some rooms. So I have a double problem: oversize boiler and undersize rads. The main hallway rad is on pretty much permanently just to maintain the zone at 19 degrees. The living room rad is too small for the room but eventually manages to get the room to 21 degrees after a few hours, although it then is also on pretty much permanently in order to maintain the temperature. The conservatory (double glazed) which serves as a dining room has a woefully undersized radiator that cannot even maintain a 15 degree set-point in this weather, so I leave it off and heat with a 3kw electric radiator during the times I need to use the room.
I'll experiment with different flow temps to check what the gas usage as. I really need to run at a higher temp to compensate for these undersized rads. I'm a little fearful of the result though, as I recall before I put in Evohome I had a gas bill of £200+ for 30 days usage in one month when running a flow temp of 65 degrees and only a few rooms in the house were actually being heated.