Page 3 of 4 FirstFirst 1234 LastLast
Results 21 to 30 of 38

Thread: evohome HCE80 UFH valve state decoding from radio signals

  1. #21
    Automated Home Legend
    Join Date
    Jul 2014
    Posts
    1,086

    Default

    You definitely have a problem with your radio and it's firmware. This log has some Heat Demand but again only for 1 UFH controller and only for 1 zone within it.

  2. #22
    Automated Home Guru
    Join Date
    Feb 2016
    Posts
    238

    Default

    @springgreens I recommend trying the 'fifo-hang' branch of the ghoti57/evofw2 firmware as this is the current active development branch. I've been testing it over the weekend with pretty good results. As Bruce has mentioned, there's definitely a problem with the firmware processing exactly the HCE80s message that you need.

  3. #23
    Automated Home Jr Member
    Join Date
    Feb 2018
    Posts
    47

    Default

    @DanD I also just tried the 'fifo-hang' branch. Zone demand data seems to be coming through fine on the HCC80R with this as well, but sending is no longer working for me (arduino nano). Rolling back to the original fifo firmware, and sending works straight away.

    Is sending working correctly for you?

  4. #24
    Automated Home Guru
    Join Date
    Feb 2016
    Posts
    238

    Default

    @smar Thanks for trying out the fifo-hang branch and confirming that it receives the HCC80R demand messages OK on your system. With regards to sending, no it's not currently functional on this branch.

  5. #25
    Automated Home Jr Member
    Join Date
    Dec 2019
    Posts
    21

    Default

    Thanks. I'll try the fifo-hang firmware. But will be later in the week

  6. #26
    Automated Home Jr Member
    Join Date
    Feb 2018
    Posts
    47

    Default

    Quote Originally Posted by DanD View Post
    With regards to sending, no it's not currently functional on this branch.
    Ok thanks for the confirmation.

  7. #27
    Automated Home Jr Member
    Join Date
    Dec 2019
    Posts
    21

    Default

    Here's part of a log fom evohome-listner script running with ghoti57/fifo-hang branch (but I had to add spi.c to the Makefile and #NEEDS_MAIN to sha_nano_v3.h)
    I've got plenty more logs but am getting php errors trying to upload - so a small part spread over 3 posts...


    The evohome config
    {
    "01:062953": { "name": "Study", "zoneId" : 1, "ufh_zoneId": 2, "zoneMaster": true },
    "30:071715": { "name": "evoGateway", "zoneId" : 240, "zoneMaster": false },
    "02:025324": { "name": "HCE80_1", "zoneId" : -1, "zoneMaster" :false },
    "02:023727": { "name": "HCE80_2", "zoneId" : -1, "zoneMaster" :false },
    "03:255727": { "name": "Living room", "zoneId" : 2, "ufh_zoneId": 0, "zoneMaster": true },
    "03:125829": { "name": "Garden room", "zoneId" : 3, "ufh_zoneId": 1, "zoneMaster": true },
    "03:125833": { "name": "Shower room", "zoneId": 5, "ufh_zoneId": 1, "zoneMaster": true },
    "03:256078": { "name": "Ensuite", "zoneId": 7, "ufh_zoneId": 3, "zoneMaster": true },
    "03:255827": { "name": "Hall", "zoneId": 4, "ufh_zoneId": 0, "zoneMaster": true },
    "03:256140": { "name": "Lounge", "zoneId": 6, "ufh_zoneId": 2, "zoneMaster": true },
    "03:125827": { "name": "New bedroom", "zoneId": 8, "ufh_zoneId": 4, "zoneMaster": true },
    "03:255832": { "name": "Bay bedroom", "zoneId": 12, "ufh_zoneId": 3, "zoneMaster": true },
    "04:146232": { "name": "HBedroom", "zoneId": 9, "zoneMaster": true },
    "04:146262": { "name": "HDayroom", "zoneId": 10, "zoneMaster": true },
    "04:160544": { "name": "HBathroom", "zoneId": 11, "zoneMaster": true },
    "13:233522": { "name": "evoHeatDemand", "zoneId" : 252, "zoneMaster" : false }
    }


    As far as I can tell the conclusion is that HCE80 doesn't transmit individual zone actuator demands, or at least we haven't so far worked out how to read them.
    Pls let me know if you think otherwise, you need more logs or different radio firmware trials. I'm very happy to support wider efforts to decode evohome radioeven if we can't figure out indiv zone demands!


    2020-01-24 23:55:55: 1: SYNC --- I --- 01:062953 --:------ 01:062953 1F09 003 FF0744
    2020-01-24 23:55:56: 1: SETPOINT_CTL --- I --- 01:062953 --:------ 01:062953 2309 036 0006810106400201F40304450406200505CA0606AD0701F408 01F40902260A06400B01F4
    2020-01-24 23:55:56: 1: ZONE_TEMPERATURE --- I --- 01:062953 --:------ 01:062953 30C9 036 00087A01085C0207D80307B204085C05078A0607800706B808 07220907490A076A0B06B8
    2020-01-24 23:56:21: 1: UNKNOWN COMMAND: --- I --- 03:125829 --:------ 03:125829 2389 003 020001
    2020-01-24 23:56:21: 1: --- I --- 03:125829 --:------ 03:125829 2389 003 020001
    2020-01-24 23:56:21: 1: EXTERNAL_SENSOR --- I --- 03:125829 --:------ 03:125829 0002 004 03020105
    2020-01-24 23:56:28: 1: ACTUATOR_CHECK_REQ --- I --- 13:233522 --:------ 13:233522 3B00 002 00C8
    2020-01-24 23:56:29: 1: ACTUATOR_STATE --- I --- 13:233522 --:------ 13:233522 3EF0 003 0000FF
    2020-01-24 23:56:30: 1: ACTUATOR_CHECK_REQ --- I --- 01:062953 --:------ 01:062953 3B00 002 FCC8
    2020-01-24 23:56:32: 1: UNKNOWN COMMAND: --- I --- 03:255727 --:------ 03:255727 2389 003 020041
    2020-01-24 23:56:32: 1: --- I --- 03:255727 --:------ 03:255727 2389 003 020041
    2020-01-24 23:56:54: 1: WINDOW_STATUS --- I --- 04:146232 --:------ 01:062953 12B0 003 080000
    2020-01-24 23:56:57: 1: WINDOW_STATUS --- I --- 04:146232 --:------ 01:062953 12B0 003 080000
    2020-01-24 23:57:10: 1: SETPOINT --- I --- 04:146232 --:------ 01:062953 2309 003 0801F4
    2020-01-24 23:58:38: 1: ZONE_TEMPERATURE --- I --- 03:255727 --:------ 03:255727 30C9 003 010870
    2020-01-24 23:58:57: 1: UNKNOWN COMMAND: --- I --- 03:255827 --:------ 03:255827 2389 003 02005D
    2020-01-24 23:58:57: 1: --- I --- 03:255827 --:------ 03:255827 2389 003 02005D
    2020-01-24 23:59:01: 1: SYNC --- I --- 01:062953 --:------ 01:062953 1F09 003 FF0744
    2020-01-24 23:59:01: 1: SETPOINT_CTL --- I --- 01:062953 --:------ 01:062953 2309 036 0006810106410201F40304450406200505CA0606AD0701F408 01F40902260A06400B01F4
    2020-01-24 23:59:01: 1: ZONE_TEMPERATURE --- I --- 01:062953 --:------ 01:062953 30C9 036 00087001085C0207C50307B204085C05078A0607800706B808 07220907490A076A0B06B8
    2020-01-25 00:00:24: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FC00
    2020-01-25 00:00:30: 1: ZONE_TEMPERATURE --- I --- 03:256078 --:------ 03:256078 30C9 003 01076C
    2020-01-25 00:01:13: 1: ZONE_HEAT_DEMAND --- I --- 04:160544 --:------ 01:062953 3150 002 0A00
    2020-01-25 00:01:29: 1: ACTUATOR_STATE --- I --- 13:233522 --:------ 13:233522 3EF0 003 0000FF
    2020-01-25 00:01:32: 1: ACTUATOR_CHECK_REQ --- I --- 01:062953 --:------ 01:062953 3B00 002 FCC8
    2020-01-25 00:02:07: 1: SYNC --- I --- 01:062953 --:------ 01:062953 1F09 003 FF0744
    2020-01-25 00:02:07: 1: SETPOINT_CTL --- I --- 01:062953 --:------ 01:062953 2309 036 0006810106410201F40304450406200505CA0606AD0701F408 01F40902260A06400B01F4
    2020-01-25 00:02:07: 1: ZONE_TEMPERATURE --- I --- 01:062953 --:------ 01:062953 30C9 036 00087001085C0207C50307B204085C05078A06076C0706B808 07220907490A076A0B06B8
    2020-01-25 00:02:35: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FC00
    2020-01-25 00:05:13: 1: SYNC --- I --- 01:062953 --:------ 01:062953 1F09 003 FF0744
    2020-01-25 00:05:13: 1: SETPOINT_CTL --- I --- 01:062953 --:------ 01:062953 2309 036 0006810106410201F40304450406200505CA0606AD0701F408 01F40902260A06400B01F4
    2020-01-25 00:05:13: 1: ZONE_TEMPERATURE --- I --- 01:062953 --:------ 01:062953 30C9 036 00087001085C0207B20307B204085C05078A06076C0706B808 07220907490A076A0B06B8
    2020-01-25 00:06:15: 1: ZONE_TEMPERATURE --- I --- 03:125829 --:------ 03:125829 30C9 003 010866
    2020-01-25 00:06:17: 1: ZONE_TEMPERATURE --- I --- 03:125833 --:------ 03:125833 30C9 003 010866
    2020-01-25 00:06:28: 1: --- I --- 13:233522 --:------ 13 :233522 3B00 002 00C8
    2020-01-25 00:06:29: 1: --- I --- 13:233522 --:------ 13 :233522 3EF0 003 0000FF
    2020-01-25 00:06:32: 1: ACTUATOR_CHECK_REQ --- I --- 01:062953 --:------ 01:062953 3B00 002 FCC8
    2020-01-25 00:06:47: 1: UNKNOWN COMMAND: --- I --- 03:256140 --:------ 03:256140 2389 003 02FF88
    2020-01-25 00:06:47: 1: --- I --- 03:256140 --:------ 03:256140 2389 003 02FF88
    2020-01-25 00:06:54: 1: ZONE_TEMPERATURE --- I --- 03:255827 --:------ 03:255827 30C9 003 0107BC
    2020-01-25 00:06:54: 1: EXTERNAL_SENSOR --- I --- 03:255827 --:------ 03:255827 0002 004 03020105
    2020-01-25 00:07:32: 1: RELAY_HEAT_DEMAND --- I --- 01:062953 --:------ 01:062953 0008 002 FC00
    2020-01-25 00:08:19: 1: SYNC --- I --- 01:062953 --:------ 01:062953 1F09 003 FF0744
    2020-01-25 00:08:19: 1: SETPOINT_CTL --- I --- 01:062953 --:------ 01:062953 2309 036 0006810106410201F40304450406200505C80606AD0701F408 01F40902260A06400B01F4
    2020-01-25 00:08:19: 1: ZONE_TEMPERATURE --- I --- 01:062953 --:------ 01:062953 30C9 036 0008700108660207BC0307BC04086605078A06076C0706B808 07220907490A076A0B06B8
    2020-01-25 00:11:25: 1: SYNC --- I --- 01:062953 --:------ 01:062953 1F09 003 FF0744
    2020-01-25 00:11:25: 1: SETPOINT_CTL --- I --- 01:062953 --:------ 01:062953 2309 036 0006810106410201F40304450406200505C80606AD0701F408 01F40902260A06400B01F4
    2020-01-25 00:11:25: 1: ZONE_TEMPERATURE --- I --- 01:062953 --:------ 01:062953 30C9 036 0008700108660207BC0307BC04086605078A06076C0706B808 07220907490A076A0B06B8
    2020-01-25 00:11:29: 1: ACTUATOR_CHECK_REQ --- I --- 13:233522 --:------ 13:233522 3B00 002 00C8
    2020-01-25 00:11:29: 1: ACTUATOR_CHECK_REQ --- I --- 01:062953 --:------ 01:062953 3B00 002 FCC8
    2020-01-25 00:11:29: 1: ACTUATOR_STATE --- I --- 13:233522 --:------ 13:233522 3EF0 003 0000FF
    2020-01-25 00:11:37: 1: ZONE_HEAT_DEMAND --- I --- 04:146232 --:------ 01:062953 3150 002 0800
    2020-01-25 00:11:38: 1: ZONE_HEAT_DEMAND --- I --- 04:146262 --:------ 01:062953 3150 002 0900
    2020-01-25 00:11:43: 1: ZONE_HEAT_DEMAND --- I --- 01:062953 --:------ 01:062953 3150 002 FC00
    2020-01-25 00:14:19: 1: UNKNOWN COMMAND: --- I --- 03:125827 --:------ 03:125827 2389 003 02FB50
    2020-01-25 00:14:19: 1: --- I --- 03:125827 --:------ 03:125827 2389 003 02FB50
    2020-01-25 00:14:31: 1: SYNC --- I --- 01:062953 --:------ 01:062953 1F09 003 FF0744
    2020-01-25 00:14:31: 1: SETPOINT_CTL --- I --- 01:062953 --:------ 01:062953 2309 036 0006810106410201F40304450406200505C80606AD0701F408 01F40902260A06400B01F4
    2020-01-25 00:14:31: 1: ZONE_TEMPERATURE --- I --- 01:062953 --:------ 01:062953 30C9 036 0008700108660207BC0307BC04086605078A06076C0706B808 07220907490A076A0B06B8
    2020-01-25 00:15:24: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FC00
    2020-01-25 00:16:24: 1: ZONE_TEMPERATURE --- I --- 03:125827 --:------ 03:125827 30C9 003 0106B8
    2020-01-25 00:16:29: 1: --- I --- 13:233522 --:------ 13 :233522 3EF0 003 0000FF
    2020-01-25 00:16:30: 1: --- I --- 13:233522 --:------ 13 :233522 3B00 002 00C8
    2020-01-25 00:16:33: 1: ACTUATOR_CHECK_REQ --- I --- 01:062953 --:------ 01:062953 3B00 002 FCC8
    2020-01-25 00:17:12: 1: ZONE_TEMPERATURE --- I --- 04:146262 --:------ 04:146262 30C9 003 000735

  8. #28
    Automated Home Jr Member
    Join Date
    Dec 2019
    Posts
    21

    Default

    2020-01-25 00:17:15: 1: Window_status --- i --- 04:146262 --:------ 01:062953 12b0 003 090000
    2020-01-25 00:17:30: 1: Setpoint --- i --- 04:146262 --:------ 01:062953 2309 003 090226
    2020-01-25 00:17:34: 1: Relay_heat_demand --- i --- 02:023727 --:------ 02:023727 0008 002 fc00
    2020-01-25 00:17:37: 1: Sync --- i --- 01:062953 --:------ 01:062953 1f09 003 ff0744
    2020-01-25 00:17:37: 1: Setpoint_ctl --- i --- 01:062953 --:------ 01:062953 2309 036 0006810106410201f40304450406200505c80606ad0701f408 01f40902260a06400b01f4
    2020-01-25 00:17:37: 1: Zone_temperature --- i --- 01:062953 --:------ 01:062953 30c9 036 0008700108660207bc0307bc04086605078a06076c0706b808 07220907350a076a0b06b8
    2020-01-25 00:20:05: 1: Window_status --- i --- 04:160544 --:------ 01:062953 12b0 003 0a0000
    2020-01-25 00:20:08: 1: Window_status --- i --- 04:160544 --:------ 01:062953 12b0 003 0a0000
    2020-01-25 00:20:18: 1: Setpoint --- i --- 04:160544 --:------ 01:062953 2309 003 0a0640
    2020-01-25 00:20:19: 1: Unknown command: --- i --- 03:125833 --:------ 03:125833 2389 003 02ffe0
    2020-01-25 00:20:19: 1: --- i --- 03:125833 --:------ 03:125833 2389 003 02ffe0
    2020-01-25 00:20:19: 1: External_sensor --- i --- 03:125833 --:------ 03:125833 0002 004 03020105
    2020-01-25 00:20:43: 1: Sync --- i --- 01:062953 --:------ 01:062953 1f09 003 ff0744
    2020-01-25 00:20:43: 1: Setpoint_ctl --- i --- 01:062953 --:------ 01:062953 2309 036 0006810106410201f40304450406200505c80606ad0701f408 01f40902260a06400b01f4
    2020-01-25 00:20:43: 1: Zone_temperature --- i --- 01:062953 --:------ 01:062953 30c9 036 0008700108660207bc0307bc04086605078a06076c0706b808 07220907350a076a0b06b8
    2020-01-25 00:21:13: 1: Zone_heat_demand --- i --- 04:160544 --:------ 01:062953 3150 002 0a00
    2020-01-25 00:21:29: 1: Actuator_state --- i --- 13:233522 --:------ 13:233522 3ef0 003 0000ff
    2020-01-25 00:21:29: 1: Actuator_check_req --- i --- 13:233522 --:------ 13:233522 3b00 002 00c8
    2020-01-25 00:21:34: 1: Actuator_check_req --- i --- 01:062953 --:------ 01:062953 3b00 002 fcc8
    2020-01-25 00:21:52: 1: Zone_temperature --- i --- 04:146232 --:------ 04:146232 30c9 003 00070d
    2020-01-25 00:23:49: 1: Sync --- i --- 01:062953 --:------ 01:062953 1f09 003 ff0744
    2020-01-25 00:23:49: 1: Setpoint_ctl --- i --- 01:062953 --:------ 01:062953 2309 036 0006810106410201f40304450406200505c80606ad0701f408 01f40902260a06400b01f4
    2020-01-25 00:23:49: 1: Zone_temperature --- i --- 01:062953 --:------ 01:062953 30c9 036 0008700108660207bc0307bc04086605078a06076c0706b808 070d0907350a076a0b06b8
    2020-01-25 00:24:37: 1: Unknown command: --- i --- 03:255832 --:------ 03:255832 2389 003 02fb64
    2020-01-25 00:24:37: 1: --- i --- 03:255832 --:------ 03:255832 2389 003 02fb64
    2020-01-25 00:24:37: 1: External_sensor --- i --- 03:255832 --:------ 03:255832 0002 004 03020105
    2020-01-25 00:26:12: 1: Zone_temperature --- i --- 04:146262 --:------ 04:146262 30c9 003 000723
    2020-01-25 00:26:29: 1: Actuator_state --- i --- 13:233522 --:------ 13:233522 3ef0 003 0000ff
    2020-01-25 00:26:29: 1: --- i --- 13:233522 --:------ 13 :233522 3b00 002 00c8
    2020-01-25 00:26:33: 1: Actuator_check_req --- i --- 01:062953 --:------ 01:062953 3b00 002 fcc8
    2020-01-25 00:26:55: 1: Sync --- i --- 01:062953 --:------ 01:062953 1f09 003 ff0744
    2020-01-25 00:26:55: 1: Setpoint_ctl --- i --- 01:062953 --:------ 01:062953 2309 036 0006810106410201f40304450406200505c80606ad0701f408 01f40902260a06400b01f4
    2020-01-25 00:26:55: 1: Zone_temperature --- i --- 01:062953 --:------ 01:062953 30c9 036 0008700108660207a70307bc04086605078a06076c0706b808 070d0907230a076a0b06b8
    2020-01-25 00:27:36: 1: Relay_heat_demand --- i --- 01:062953 --:------ 01:062953 0008 002 fc00
    2020-01-25 00:30:01: 1: Sync --- i --- 01:062953 --:------ 01:062953 1f09 003 ff0744
    2020-01-25 00:30:01: 1: Zone_info --- i --- 01:062953 --:------ 01:062953 000a 048 001401f40dac011401f40dac021001f40dac031401f40dac04 1401f40dac051401f40dac061401f40dac071401f40dac
    2020-01-25 00:30:01: 1: Zone_info --- i --- 01:062953 --:------ 01:062953 000a 024 081001f40dac091001f40dac0a1001f40dac0b1401f40dac
    2020-01-25 00:30:05: 1: Zone_temperature --- i --- 04:160544 --:------ 04:160544 30c9 003 000756
    2020-01-25 00:30:23: 1: Relay_heat_demand --- i --- 02:025324 --:------ 02:025324 0008 002 fc00
    2020-01-25 00:30:48: 1: External_sensor --- i --- 03:256140 --:------ 03:256140 0002 004 03020105
    2020-01-25 00:31:29: 1: Actuator_state --- i --- 13:233522 --:------ 13:233522 3ef0 003 0000ff
    2020-01-25 00:31:31: 1: Actuator_check_req --- i --- 01:062953 --:------ 01:062953 3b00 002 fcc8
    2020-01-25 00:31:38: 1: Zone_heat_demand --- i --- 04:146232 --:------ 01:062953 3150 002 0800
    2020-01-25 00:31:38: 1: Zone_heat_demand --- i --- 04:146262 --:------ 01:062953 3150 002 0900
    2020-01-25 00:31:43: 1: Zone_heat_demand --- i --- 01:062953 --:------ 01:062953 3150 002 fc00
    2020-01-25 00:32:14: 1: Zone_temperature --- i --- 04:146262 --:------ 04:146262 30c9 003 00070e
    2020-01-25 00:32:34: 1: Relay_heat_demand --- i --- 02:023727 --:------ 02:023727 0008 002 fc00
    2020-01-25 00:32:53: 1: Zone_temperature --- i --- 04:146232 --:------ 04:146232 30c9 003 0006fa
    2020-01-25 00:33:07: 1: Sync --- i --- 01:062953 --:------ 01:062953 1f09 003 ff0744
    2020-01-25 00:33:07: 1: Setpoint_ctl --- i --- 01:062953 --:------ 01:062953 2309 036 0006810106410201f40304450406200505c80606ad0701f408 01f40902260a06400b01f4
    2020-01-25 00:33:07: 1: Zone_temperature --- i --- 01:062953 --:------ 01:062953 30c9 036 0008700108660207b10307bc04086605078a06076c0706b808 06fa09070e0a07560b06b8
    2020-01-25 00:34:30: 1: Unknown command: --- i --- 03:256078 --:------ 03:256078 2389 003 02006f
    2020-01-25 00:34:30: 1: --- i --- 03:256078 --:------ 03:256078 2389 003 02006f
    2020-01-25 00:34:49: 1: Zone_temperature --- i --- 03:256140 --:------ 03:256140 30c9 003 01079e
    2020-01-25 00:36:13: 1: Sync --- i --- 01:062953 --:------ 01:062953 1f09 003 ff0744
    2020-01-25 00:36:13: 1: Setpoint_ctl --- i --- 01:062953 --:------ 01:062953 2309 036 0006810106410201f40304450406200505c80606af0701f408 01f40902260a06400b01f4
    2020-01-25 00:36:13: 1: Zone_temperature --- i --- 01:062953 --:------ 01:062953 30c9 036 0008700108660207b10307bc04086605079e06076c0706b808 06fa09070e0a07560b06b8
    2020-01-25 00:36:29: 1: --- i --- 13:233522 --:------ 13 :233522 3ef0 003 0000ff
    2020-01-25 00:36:29: 1: Actuator_check_req --- i --- 13:233522 --:------ 13:233522 3b00 002 00c8
    2020-01-25 00:36:32: 1: External_sensor --- i --- 03:256078 --:------ 03:256078 0002 004 03020105
    2020-01-25 00:36:32: 1: Actuator_check_req --- i --- 01:062953 --:------ 01:062953 3b00 002 fcc8
    2020-01-25 00:38:21: 1: External_sensor --- i --- 03:125827 --:------ 03:125827 0002 004 03020105
    2020-01-25 00:39:04: 1: Zone_temperature --- i --- 04:160544 --:------ 04:160544 30c9 003 000741
    2020-01-25 00:39:19: 1: Sync --- i --- 01:062953 --:------ 01:062953 1f09 003 ff0744
    2020-01-25 00:39:19: 1: Setpoint_ctl --- i --- 01:062953 --:------ 01:062953 2309 036 0006810106410201f40304450406200505c80606af0701f408 01f40902260a06400b01f4
    2020-01-25 00:39:19: 1: Zone_temperature --- i --- 01:062953 --:------ 01:062953 30c9 036 0008700108660207b10307bc04086605079e06076c0706b808 06fa09070e0a07410b06b8
    2020-01-25 00:40:53: 1: Zone_temperature --- i --- 04:146232 --:------ 04:146232 30c9 003 0006e8
    2020-01-25 00:41:16: 1: Zone_heat_demand --- i --- 04:160544 --:------ 01:062953 3150 002 0a00
    2020-01-25 00:41:29: 1: Actuator_check_req --- i --- 13:233522 --:------ 13:233522 3b00 002 00c8
    2020-01-25 00:41:29: 1: Actuator_check_req --- i --- 01:062953 --:------ 01:062953 3b00 002 fcc8
    2020-01-25 00:42:25: 1: Sync --- i --- 01:062953 --:------ 01:062953 1f09 003 ff0744
    2020-01-25 00:42:25: 1: Setpoint_ctl --- i --- 01:062953 --:------ 01:062953 2309 036 0006810106410201f40304450406200505c80606af0701f408 01f40902260a06400b01f4
    2020-01-25 00:42:25: 1: Zone_temperature --- i --- 01:062953 --:------ 01:062953 30c9 036 0008700108660207b10307bc04086605079e06076c0706b808 06e809070e0a07410b06b8
    2020-01-25 00:43:44: 1: Actuator_state --- rq --- 01:062953 13:233522 --:------ 3ef0 001 00
    2020-01-25 00:43:46: 1: Actuator_state --- rq --- 01:062953 13:233522 --:------ 3ef0 001 00
    2020-01-25 00:43:48: 1: Actuator_state --- rq --- 01:062953 13:233522 --:------ 3ef0 001 00
    2020-01-25 00:45:13: 1: Zone_temperature --- i --- 04:146262 --:------ 04:146262 30c9 003 0006fb
    2020-01-25 00:45:31: 1: Sync --- i --- 01:062953 --:------ 01:062953 1f09 003 ff0744
    2020-01-25 00:45:31: 1: Setpoint_ctl --- i --- 01:062953 --:------ 01:062953 2309 036 0006810106410201f40304450406200505c80606af0701f408 01f40902260a06400b01f4
    2020-01-25 00:45:31: 1: Zone_temperature --- i --- 01:062953 --:------ 01:062953 30c9 036 0008700108660207b10307bc04086605079e06076c0706b808 06e80906fb0a07410b06b8
    2020-01-25 00:46:29: 1: Actuator_check_req --- i --- 13:233522 --:------ 13:233522 3b00 002 00c8
    2020-01-25 00:46:29: 1: Actuator_state --- i --- 13:233522 --:------ 13:233522 3ef0 003 0000ff
    2020-01-25 00:46:33: 1: Actuator_check_req --- i --- 01:062953 --:------ 01:062953 3b00 002 fcc8
    2020-01-25 00:47:34: 1: Relay_heat_demand --- i --- 02:023727 --:------ 02:023727 0008 002 fc00
    2020-01-25 00:47:40: 1: Relay_heat_demand --- i --- 01:062953 --:------ 01:062953 0008 002 fc00

  9. #29
    Automated Home Legend
    Join Date
    Jul 2014
    Posts
    1,086

    Default

    Can you please show us evidence that the controller can show the heat demand from the individual zones of the UFH controller.

  10. #30
    Automated Home Jr Member
    Join Date
    Feb 2018
    Posts
    47

    Default

    Quote Originally Posted by bruce_miranda View Post
    Can you please show us evidence that the controller can show the heat demand from the individual zones of the UFH controller.
    Here's a couple of lines (filtered out to show just the 02: messages):

    Raw:
    Code:
    2020-01-26 08:26:21 |1| ZONE_HEAT_DEMAND   ---  I --- 02:043392 --:------ 02:043392 3150 006 00AC01BA029C
    2020-01-26 08:41:21 |1| ZONE_HEAT_DEMAND   ---  I --- 02:043392 --:------ 01:139901 3150 002 0B9A
    Decoded:
    Code:
    2020-01-26 08:26:21 |1| ZONE_HEAT_DEMAND    | I | UFH Controller        -> BROADCAST MESSAGE     |   86.0% @ Dining room          [Zone 8  ] 
    2020-01-26 08:26:21 |1| ZONE_HEAT_DEMAND    | I | UFH Controller        -> BROADCAST MESSAGE     |   93.0% @ Kitchen UFH          [Zone 11 ] 
    2020-01-26 08:26:21 |1| ZONE_HEAT_DEMAND    | I | UFH Controller        -> BROADCAST MESSAGE     |   78.0% @ Hallway              [Zone 12 ] 
    2020-01-26 08:41:21 |1| ZONE_HEAT_DEMAND    | I | UFH Controller        -> CONTROLLER            |   77.0% @ Hallway              [Zone 12 ]

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •