evohome HCE80 UFH valve state decoding from radio signals

Collapse
X
 
  • Filter
  • Time
  • Show
Clear All
new posts
  • bruce_miranda
    Automated Home Legend
    • Jul 2014
    • 2309

    #16
    The weird thing is that there were absolutely NO messages from your UFH controller in the dump that you added earlier. I don't know over what time period that dump was taken but I would have expected atleast some messages from the 02: devices if the HCE80 is indeed an 02: device like the HCC80R. It doesn't matter if you added more zones now, what would be good is to have ALL raw radio messages captured for about 4 hours. Put it in the file and upload that file somewhere so Dan and I can have a look at it. Your installation is quite interesting as a case study. We don't see many HCE80s.
    I actually think the HCE80 is summing up the Heat Demand for the entire controller and sending it to the Evohome as a single Heat Demand single. And this is exactly why I have been asking to see the System Summary page for your controller. Because if that page cannot show the individual zone Heat Demands, then there is no way we can. I have been able to find everything else in your dump i.e. zone temps, set points, upper and lower maxs etc. But not the individual heat demands.

    P.S. Relooked at the other thread. You defined 30:071715": { "name" : "evoGateway", "zoneId" : 240, "zoneMaster" : false} Why ? You have the V3 of the controller which doesn't need an Internet Gateway.
    Last edited by bruce_miranda; 19 January 2020, 09:32 PM.

    Comment

    • Springgreens
      Automated Home Jr Member
      • Dec 2019
      • 21

      #17
      Yes, I see what you mean. Actually it ran all night and I just looked at the log file - same as extract above there are no 02: messages at all.
      I definitialy had some earlier. Have switched back to the ghoti57/master branch firmware and will set a recording going again later. I'm away tomorroy and back quite late Tuesday so may be wednesday evening before I can get the results to you.

      Comment

      • smar
        Automated Home Sr Member
        • Feb 2018
        • 57

        #18
        Originally posted by Springgreens View Post
        Yes, I see what you mean. Actually it ran all night and I just looked at the log file - same as extract above there are no 02: messages at all.
        I definitialy had some earlier. Have switched back to the ghoti57/master branch firmware and will set a recording going again later. I'm away tomorroy and back quite late Tuesday so may be wednesday evening before I can get the results to you.
        I recall when I was testing with one of ghoti's firmwares (I think the master) I wasn't receiving any messages from my HCC80R. Switching to the other fifo branch, the messages immediately started coming through (or possibly the other way round!).

        Comment

        • smar
          Automated Home Sr Member
          • Feb 2018
          • 57

          #19
          Originally posted by bruce_miranda View Post

          P.S. Relooked at the other thread. You defined 30:071715": { "name" : "evoGateway", "zoneId" : 240, "zoneMaster" : false} Why ? You have the V3 of the controller which doesn't need an Internet Gateway.
          That's actually the way I've done the script - when sending messages, it sends it from that 30: id, so that the evohome controller thinks it is getting a valid instruction from an internet gateway.

          Comment

          • Springgreens
            Automated Home Jr Member
            • Dec 2019
            • 21

            #20
            Here's a log I had from a few days over last week. Recorded with smar's listener python & ghoti57 master branch firmware.
            I gave up trying to upload either zip or txt. Here's messages filtered for '- 02:'
            I guess all too short to contain individual zone info?

            ther's repeated messages below just becasue of the way notepad++ search works - check the line numbers

            Line 506: 2020-01-16 03:22:43: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FC00
            Line 507: 2020-01-16 03:24:09: 1: --- I --- 02:023727 *ERR_BAD_STOP_BIT*
            Line 517: 2020-01-16 03:31:19: 1: --- I --- 02:025324 --:------ 02:025324 *ERR_BAD_STOP_BIT*
            Line 517: 2020-01-16 03:31:19: 1: --- I --- 02:025324 --:------ 02:025324 *ERR_BAD_STOP_BIT*
            Line 526: 2020-01-16 03:34:43: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FC00
            Line 526: 2020-01-16 03:34:43: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FC00
            Line 527: 2020-01-16 03:36:13: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FC00
            Line 527: 2020-01-16 03:36:13: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FC00
            Line 530: 2020-01-16 03:38:55: 1: ZONE_HEAT_DEMAND --- I --- 02:023727 --:------ 01:062953 3150 002 0364
            Line 536: 2020-01-16 03:43:19: 1: --- I --- 02:025324 --:------ *ERR_BAD_STOP_BIT*
            Line 540: 2020-01-16 03:43:59: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FCC8
            Line 540: 2020-01-16 03:43:59: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FCC8
            Line 545: 2020-01-16 03:48:16: 1: --- I --- 02:023727 --:------ 02:023727 *ERR_BAD_STOP_BIT*
            Line 545: 2020-01-16 03:48:16: 1: --- I --- 02:023727 --:------ 02:023727 *ERR_BAD_STOP_BIT*
            Line 556: 2020-01-16 03:53:54: 1: --- I --- 02:023727 --:------ *ERR_BAD_STOP_BIT*
            Line 558: 2020-01-16 03:55:19: 1: --- I --- 02:025324 --:------ 02:025324 0008 002 FCC8 *ERR_BAD_STOP_BIT*
            Line 558: 2020-01-16 03:55:19: 1: --- I --- 02:025324 --:------ 02:025324 0008 002 FCC8 *ERR_BAD_STOP_BIT*
            Line 559: 2020-01-16 03:56:03: 1: --- I --- 02:023727 *ERR_BAD_STOP_BIT*
            Line 566: 2020-01-16 04:00:20: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FC00
            Line 566: 2020-01-16 04:00:20: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FC00
            Line 586: 2020-01-16 04:08:07: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FCC8
            Line 586: 2020-01-16 04:08:07: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FCC8
            Line 590: 2020-01-16 04:08:54: 1: ZONE_HEAT_DEMAND --- I --- 02:023727 --:------ 01:062953 3150 002 0364
            Line 591: 2020-01-16 04:10:42: 1: --- I --- 02:025324 --:------ 02:025324 *ERR_BAD_STOP_BIT*
            Line 591: 2020-01-16 04:10:42: 1: --- I --- 02:025324 --:------ 02:025324 *ERR_BAD_STOP_BIT*
            Line 599: 2020-01-16 04:12:24: 1: --- I --- 02:023727 --:------ *ERR_BAD_STOP_BIT*
            Line 607: 2020-01-16 04:20:11: 1: --- I --- 02:023727 --:------ *ERR_BAD_STOP_BIT*
            Line 615: 2020-01-16 04:23:54: 1: --- I --- 02:023727 --:------ 01:062953 3150 002 03 *ERR_BAD_STOP_BIT*
            Line 619: 2020-01-16 04:24:28: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FC00
            Line 619: 2020-01-16 04:24:28: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FC00
            Line 629: 2020-01-16 04:31:18: 1: --- I --- 02:025324 --:------ 02:025324 0008 002 FCC8 *ERR_BAD_STOP_BIT*
            Line 629: 2020-01-16 04:31:18: 1: --- I --- 02:025324 --:------ 02:025324 0008 002 FCC8 *ERR_BAD_STOP_BIT*
            Line 631: 2020-01-16 04:32:15: 1: --- I --- 02:023727 --:------ *ERR_BAD_STOP_BIT*
            Line 640: 2020-01-16 04:38:54: 1: ZONE_HEAT_DEMAND --- I --- 02:023727 --:------ 01:062953 3150 002 0364
            Line 649: 2020-01-16 04:43:18: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FCC8
            Line 649: 2020-01-16 04:43:18: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FCC8
            Line 650: 2020-01-16 04:44:19: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FCC8
            Line 650: 2020-01-16 04:44:19: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FCC8
            Line 654: 2020-01-16 04:46:42: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FC00
            Line 654: 2020-01-16 04:46:42: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FC00
            Line 665: 2020-01-16 04:53:54: 1: --- I --- 02:023727 --:------ *ERR_BAD_STOP_BIT*
            Line 670: 2020-01-16 04:55:18: 1: --- I --- 02:025324 --:------ 02:025324 *ERR_BAD_STOP_BIT*
            Line 670: 2020-01-16 04:55:18: 1: --- I --- 02:025324 --:------ 02:025324 *ERR_BAD_STOP_BIT*
            Line 679: 2020-01-16 05:00:40: 1: --- I --- 02:023727 --:------ 02:023727 *ERR_BAD_STOP_BIT*
            Line 679: 2020-01-16 05:00:40: 1: --- I --- 02:023727 --:------ 02:023727 *ERR_BAD_STOP_BIT*
            Line 696: 2020-01-16 05:07:18: 1: --- I --- 02:025324 --:------ 02:025324 *ERR_BAD_STOP_BIT*
            Line 696: 2020-01-16 05:07:18: 1: --- I --- 02:025324 --:------ 02:025324 *ERR_BAD_STOP_BIT*
            Line 700: 2020-01-16 05:08:27: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FCC8
            Line 700: 2020-01-16 05:08:27: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FCC8
            Line 701: 2020-01-16 05:08:54: 1: ZONE_HEAT_DEMAND --- I --- 02:023727 --:------ 01:062953 3150 002 0364
            Line 705: 2020-01-16 05:10:42: 1: --- I --- 02:025324 --:------ 02:025324 *ERR_BAD_STOP_BIT*
            Line 705: 2020-01-16 05:10:42: 1: --- I --- 02:025324 --:------ 02:025324 *ERR_BAD_STOP_BIT*
            Line 710: 2020-01-16 05:12:44: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FC00
            Line 710: 2020-01-16 05:12:44: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FC00
            Line 718: 2020-01-16 05:19:18: 1: --- I --- 02:025324 --:------ *ERR_BAD_STOP_BIT*
            Line 725: 2020-01-16 05:22:42: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FC00
            Line 725: 2020-01-16 05:22:42: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FC00
            Line 729: 2020-01-16 05:24:48: 1: --- I --- 02:023727 --:------ 02:023727 0008 002 FC *ERR_BAD_STOP_BIT*
            Line 729: 2020-01-16 05:24:48: 1: --- I --- 02:023727 --:------ 02:023727 0008 002 FC *ERR_BAD_STOP_BIT*
            Line 739: 2020-01-16 05:31:18: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FCC8
            Line 739: 2020-01-16 05:31:18: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FCC8
            Line 744: 2020-01-16 05:32:35: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FCC8
            Line 744: 2020-01-16 05:32:35: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FCC8
            Line 746: 2020-01-16 05:34:42: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FC00
            Line 746: 2020-01-16 05:34:42: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FC00
            Line 750: 2020-01-16 05:36:52: 1: --- I --- 02:023727 --:------ 02:023727 *ERR_BAD_STOP_BIT*
            Line 750: 2020-01-16 05:36:52: 1: --- I --- 02:023727 --:------ 02:023727 *ERR_BAD_STOP_BIT*
            Line 754: 2020-01-16 05:38:53: 1: --- I --- 02:023727 --:------ *ERR_BAD_STOP_BIT*
            Line 760: 2020-01-16 05:43:18: 1: --- I --- 02:025324 --:------ 02:025324 *ERR_BAD_STOP_BIT*
            Line 760: 2020-01-16 05:43:18: 1: --- I --- 02:025324 --:------ 02:025324 *ERR_BAD_STOP_BIT*
            Line 761: 2020-01-16 05:44:38: 1: --- I --- 02:023727 --:------ *ERR_BAD_STOP_BIT*
            Line 765: 2020-01-16 05:46:42: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FC00
            Line 765: 2020-01-16 05:46:42: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FC00
            Line 776: 2020-01-16 05:53:53: 1: --- I --- 02:023727 --:------ 01:062953 3150 002 0364 *ERR_BAD_STOP_BIT*
            Line 781: 2020-01-16 05:55:18: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FCC8
            Line 781: 2020-01-16 05:55:18: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FCC8
            Line 782: 2020-01-16 05:56:42: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FCC8
            Line 782: 2020-01-16 05:56:42: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FCC8
            Line 786: 2020-01-16 05:58:42: 1: --- I --- 02:025324 --:------ 02:025324 0008 002 FC *ERR_BAD_STOP_BIT*
            Line 786: 2020-01-16 05:58:42: 1: --- I --- 02:025324 --:------ 02:025324 0008 002 FC *ERR_BAD_STOP_BIT*
            Line 796: 2020-01-16 06:00:59: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FC00
            Line 796: 2020-01-16 06:00:59: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FC00
            Line 811: 2020-01-16 06:07:17: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FCC8
            Line 811: 2020-01-16 06:07:17: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FCC8
            Line 813: 2020-01-16 06:08:53: 1: ZONE_HEAT_DEMAND --- I --- 02:023727 --:------ 01:062953 3150 002 0364
            Line 824: 2020-01-16 06:13:03: 1: --- I --- 02:023727 --:------ 02:023727 *ERR_BAD_STOP_BIT*
            Line 824: 2020-01-16 06:13:03: 1: --- I --- 02:023727 --:------ 02:023727 *ERR_BAD_STOP_BIT*
            Line 832: 2020-01-16 06:19:17: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FCC8
            Line 832: 2020-01-16 06:19:17: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FCC8
            Line 833: 2020-01-16 06:20:50: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FCC8
            Line 833: 2020-01-16 06:20:50: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FCC8

            Comment

            • bruce_miranda
              Automated Home Legend
              • Jul 2014
              • 2309

              #21
              You definitely have a problem with your radio and it's firmware. This log has some Heat Demand but again only for 1 UFH controller and only for 1 zone within it.

              Comment

              • DanD
                Automated Home Ninja
                • Feb 2016
                • 250

                #22
                @springgreens I recommend trying the 'fifo-hang' branch of the ghoti57/evofw2 firmware as this is the current active development branch. I've been testing it over the weekend with pretty good results. As Bruce has mentioned, there's definitely a problem with the firmware processing exactly the HCE80s message that you need.

                Comment

                • smar
                  Automated Home Sr Member
                  • Feb 2018
                  • 57

                  #23
                  @DanD I also just tried the 'fifo-hang' branch. Zone demand data seems to be coming through fine on the HCC80R with this as well, but sending is no longer working for me (arduino nano). Rolling back to the original fifo firmware, and sending works straight away.

                  Is sending working correctly for you?

                  Comment

                  • DanD
                    Automated Home Ninja
                    • Feb 2016
                    • 250

                    #24
                    @smar Thanks for trying out the fifo-hang branch and confirming that it receives the HCC80R demand messages OK on your system. With regards to sending, no it's not currently functional on this branch.

                    Comment

                    • Springgreens
                      Automated Home Jr Member
                      • Dec 2019
                      • 21

                      #25
                      Thanks. I'll try the fifo-hang firmware. But will be later in the week

                      Comment

                      • smar
                        Automated Home Sr Member
                        • Feb 2018
                        • 57

                        #26
                        Originally posted by DanD View Post
                        With regards to sending, no it's not currently functional on this branch.
                        Ok thanks for the confirmation.

                        Comment

                        • Springgreens
                          Automated Home Jr Member
                          • Dec 2019
                          • 21

                          #27
                          Here's part of a log fom evohome-listner script running with ghoti57/fifo-hang branch (but I had to add spi.c to the Makefile and #NEEDS_MAIN to sha_nano_v3.h)
                          I've got plenty more logs but am getting php errors trying to upload - so a small part spread over 3 posts...


                          The evohome config
                          {
                          "01:062953": { "name": "Study", "zoneId" : 1, "ufh_zoneId": 2, "zoneMaster": true },
                          "30:071715": { "name": "evoGateway", "zoneId" : 240, "zoneMaster": false },
                          "02:025324": { "name": "HCE80_1", "zoneId" : -1, "zoneMaster" :false },
                          "02:023727": { "name": "HCE80_2", "zoneId" : -1, "zoneMaster" :false },
                          "03:255727": { "name": "Living room", "zoneId" : 2, "ufh_zoneId": 0, "zoneMaster": true },
                          "03:125829": { "name": "Garden room", "zoneId" : 3, "ufh_zoneId": 1, "zoneMaster": true },
                          "03:125833": { "name": "Shower room", "zoneId": 5, "ufh_zoneId": 1, "zoneMaster": true },
                          "03:256078": { "name": "Ensuite", "zoneId": 7, "ufh_zoneId": 3, "zoneMaster": true },
                          "03:255827": { "name": "Hall", "zoneId": 4, "ufh_zoneId": 0, "zoneMaster": true },
                          "03:256140": { "name": "Lounge", "zoneId": 6, "ufh_zoneId": 2, "zoneMaster": true },
                          "03:125827": { "name": "New bedroom", "zoneId": 8, "ufh_zoneId": 4, "zoneMaster": true },
                          "03:255832": { "name": "Bay bedroom", "zoneId": 12, "ufh_zoneId": 3, "zoneMaster": true },
                          "04:146232": { "name": "HBedroom", "zoneId": 9, "zoneMaster": true },
                          "04:146262": { "name": "HDayroom", "zoneId": 10, "zoneMaster": true },
                          "04:160544": { "name": "HBathroom", "zoneId": 11, "zoneMaster": true },
                          "13:233522": { "name": "evoHeatDemand", "zoneId" : 252, "zoneMaster" : false }
                          }


                          As far as I can tell the conclusion is that HCE80 doesn't transmit individual zone actuator demands, or at least we haven't so far worked out how to read them.
                          Pls let me know if you think otherwise, you need more logs or different radio firmware trials. I'm very happy to support wider efforts to decode evohome radioeven if we can't figure out indiv zone demands!


                          2020-01-24 23:55:55: 1: SYNC --- I --- 01:062953 --:------ 01:062953 1F09 003 FF0744
                          2020-01-24 23:55:56: 1: SETPOINT_CTL --- I --- 01:062953 --:------ 01:062953 2309 036 0006810106400201F40304450406200505CA0606AD0701F408 01F40902260A06400B01F4
                          2020-01-24 23:55:56: 1: ZONE_TEMPERATURE --- I --- 01:062953 --:------ 01:062953 30C9 036 00087A01085C0207D80307B204085C05078A0607800706B808 07220907490A076A0B06B8
                          2020-01-24 23:56:21: 1: UNKNOWN COMMAND: --- I --- 03:125829 --:------ 03:125829 2389 003 020001
                          2020-01-24 23:56:21: 1: --- I --- 03:125829 --:------ 03:125829 2389 003 020001
                          2020-01-24 23:56:21: 1: EXTERNAL_SENSOR --- I --- 03:125829 --:------ 03:125829 0002 004 03020105
                          2020-01-24 23:56:28: 1: ACTUATOR_CHECK_REQ --- I --- 13:233522 --:------ 13:233522 3B00 002 00C8
                          2020-01-24 23:56:29: 1: ACTUATOR_STATE --- I --- 13:233522 --:------ 13:233522 3EF0 003 0000FF
                          2020-01-24 23:56:30: 1: ACTUATOR_CHECK_REQ --- I --- 01:062953 --:------ 01:062953 3B00 002 FCC8
                          2020-01-24 23:56:32: 1: UNKNOWN COMMAND: --- I --- 03:255727 --:------ 03:255727 2389 003 020041
                          2020-01-24 23:56:32: 1: --- I --- 03:255727 --:------ 03:255727 2389 003 020041
                          2020-01-24 23:56:54: 1: WINDOW_STATUS --- I --- 04:146232 --:------ 01:062953 12B0 003 080000
                          2020-01-24 23:56:57: 1: WINDOW_STATUS --- I --- 04:146232 --:------ 01:062953 12B0 003 080000
                          2020-01-24 23:57:10: 1: SETPOINT --- I --- 04:146232 --:------ 01:062953 2309 003 0801F4
                          2020-01-24 23:58:38: 1: ZONE_TEMPERATURE --- I --- 03:255727 --:------ 03:255727 30C9 003 010870
                          2020-01-24 23:58:57: 1: UNKNOWN COMMAND: --- I --- 03:255827 --:------ 03:255827 2389 003 02005D
                          2020-01-24 23:58:57: 1: --- I --- 03:255827 --:------ 03:255827 2389 003 02005D
                          2020-01-24 23:59:01: 1: SYNC --- I --- 01:062953 --:------ 01:062953 1F09 003 FF0744
                          2020-01-24 23:59:01: 1: SETPOINT_CTL --- I --- 01:062953 --:------ 01:062953 2309 036 0006810106410201F40304450406200505CA0606AD0701F408 01F40902260A06400B01F4
                          2020-01-24 23:59:01: 1: ZONE_TEMPERATURE --- I --- 01:062953 --:------ 01:062953 30C9 036 00087001085C0207C50307B204085C05078A0607800706B808 07220907490A076A0B06B8
                          2020-01-25 00:00:24: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FC00
                          2020-01-25 00:00:30: 1: ZONE_TEMPERATURE --- I --- 03:256078 --:------ 03:256078 30C9 003 01076C
                          2020-01-25 00:01:13: 1: ZONE_HEAT_DEMAND --- I --- 04:160544 --:------ 01:062953 3150 002 0A00
                          2020-01-25 00:01:29: 1: ACTUATOR_STATE --- I --- 13:233522 --:------ 13:233522 3EF0 003 0000FF
                          2020-01-25 00:01:32: 1: ACTUATOR_CHECK_REQ --- I --- 01:062953 --:------ 01:062953 3B00 002 FCC8
                          2020-01-25 00:02:07: 1: SYNC --- I --- 01:062953 --:------ 01:062953 1F09 003 FF0744
                          2020-01-25 00:02:07: 1: SETPOINT_CTL --- I --- 01:062953 --:------ 01:062953 2309 036 0006810106410201F40304450406200505CA0606AD0701F408 01F40902260A06400B01F4
                          2020-01-25 00:02:07: 1: ZONE_TEMPERATURE --- I --- 01:062953 --:------ 01:062953 30C9 036 00087001085C0207C50307B204085C05078A06076C0706B808 07220907490A076A0B06B8
                          2020-01-25 00:02:35: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FC00
                          2020-01-25 00:05:13: 1: SYNC --- I --- 01:062953 --:------ 01:062953 1F09 003 FF0744
                          2020-01-25 00:05:13: 1: SETPOINT_CTL --- I --- 01:062953 --:------ 01:062953 2309 036 0006810106410201F40304450406200505CA0606AD0701F408 01F40902260A06400B01F4
                          2020-01-25 00:05:13: 1: ZONE_TEMPERATURE --- I --- 01:062953 --:------ 01:062953 30C9 036 00087001085C0207B20307B204085C05078A06076C0706B808 07220907490A076A0B06B8
                          2020-01-25 00:06:15: 1: ZONE_TEMPERATURE --- I --- 03:125829 --:------ 03:125829 30C9 003 010866
                          2020-01-25 00:06:17: 1: ZONE_TEMPERATURE --- I --- 03:125833 --:------ 03:125833 30C9 003 010866
                          2020-01-25 00:06:28: 1: --- I --- 13:233522 --:------ 13 :233522 3B00 002 00C8
                          2020-01-25 00:06:29: 1: --- I --- 13:233522 --:------ 13 :233522 3EF0 003 0000FF
                          2020-01-25 00:06:32: 1: ACTUATOR_CHECK_REQ --- I --- 01:062953 --:------ 01:062953 3B00 002 FCC8
                          2020-01-25 00:06:47: 1: UNKNOWN COMMAND: --- I --- 03:256140 --:------ 03:256140 2389 003 02FF88
                          2020-01-25 00:06:47: 1: --- I --- 03:256140 --:------ 03:256140 2389 003 02FF88
                          2020-01-25 00:06:54: 1: ZONE_TEMPERATURE --- I --- 03:255827 --:------ 03:255827 30C9 003 0107BC
                          2020-01-25 00:06:54: 1: EXTERNAL_SENSOR --- I --- 03:255827 --:------ 03:255827 0002 004 03020105
                          2020-01-25 00:07:32: 1: RELAY_HEAT_DEMAND --- I --- 01:062953 --:------ 01:062953 0008 002 FC00
                          2020-01-25 00:08:19: 1: SYNC --- I --- 01:062953 --:------ 01:062953 1F09 003 FF0744
                          2020-01-25 00:08:19: 1: SETPOINT_CTL --- I --- 01:062953 --:------ 01:062953 2309 036 0006810106410201F40304450406200505C80606AD0701F408 01F40902260A06400B01F4
                          2020-01-25 00:08:19: 1: ZONE_TEMPERATURE --- I --- 01:062953 --:------ 01:062953 30C9 036 0008700108660207BC0307BC04086605078A06076C0706B808 07220907490A076A0B06B8
                          2020-01-25 00:11:25: 1: SYNC --- I --- 01:062953 --:------ 01:062953 1F09 003 FF0744
                          2020-01-25 00:11:25: 1: SETPOINT_CTL --- I --- 01:062953 --:------ 01:062953 2309 036 0006810106410201F40304450406200505C80606AD0701F408 01F40902260A06400B01F4
                          2020-01-25 00:11:25: 1: ZONE_TEMPERATURE --- I --- 01:062953 --:------ 01:062953 30C9 036 0008700108660207BC0307BC04086605078A06076C0706B808 07220907490A076A0B06B8
                          2020-01-25 00:11:29: 1: ACTUATOR_CHECK_REQ --- I --- 13:233522 --:------ 13:233522 3B00 002 00C8
                          2020-01-25 00:11:29: 1: ACTUATOR_CHECK_REQ --- I --- 01:062953 --:------ 01:062953 3B00 002 FCC8
                          2020-01-25 00:11:29: 1: ACTUATOR_STATE --- I --- 13:233522 --:------ 13:233522 3EF0 003 0000FF
                          2020-01-25 00:11:37: 1: ZONE_HEAT_DEMAND --- I --- 04:146232 --:------ 01:062953 3150 002 0800
                          2020-01-25 00:11:38: 1: ZONE_HEAT_DEMAND --- I --- 04:146262 --:------ 01:062953 3150 002 0900
                          2020-01-25 00:11:43: 1: ZONE_HEAT_DEMAND --- I --- 01:062953 --:------ 01:062953 3150 002 FC00
                          2020-01-25 00:14:19: 1: UNKNOWN COMMAND: --- I --- 03:125827 --:------ 03:125827 2389 003 02FB50
                          2020-01-25 00:14:19: 1: --- I --- 03:125827 --:------ 03:125827 2389 003 02FB50
                          2020-01-25 00:14:31: 1: SYNC --- I --- 01:062953 --:------ 01:062953 1F09 003 FF0744
                          2020-01-25 00:14:31: 1: SETPOINT_CTL --- I --- 01:062953 --:------ 01:062953 2309 036 0006810106410201F40304450406200505C80606AD0701F408 01F40902260A06400B01F4
                          2020-01-25 00:14:31: 1: ZONE_TEMPERATURE --- I --- 01:062953 --:------ 01:062953 30C9 036 0008700108660207BC0307BC04086605078A06076C0706B808 07220907490A076A0B06B8
                          2020-01-25 00:15:24: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FC00
                          2020-01-25 00:16:24: 1: ZONE_TEMPERATURE --- I --- 03:125827 --:------ 03:125827 30C9 003 0106B8
                          2020-01-25 00:16:29: 1: --- I --- 13:233522 --:------ 13 :233522 3EF0 003 0000FF
                          2020-01-25 00:16:30: 1: --- I --- 13:233522 --:------ 13 :233522 3B00 002 00C8
                          2020-01-25 00:16:33: 1: ACTUATOR_CHECK_REQ --- I --- 01:062953 --:------ 01:062953 3B00 002 FCC8
                          2020-01-25 00:17:12: 1: ZONE_TEMPERATURE --- I --- 04:146262 --:------ 04:146262 30C9 003 000735

                          Comment

                          • Springgreens
                            Automated Home Jr Member
                            • Dec 2019
                            • 21

                            #28
                            2020-01-25 00:17:15: 1: Window_status --- i --- 04:146262 --:------ 01:062953 12b0 003 090000
                            2020-01-25 00:17:30: 1: Setpoint --- i --- 04:146262 --:------ 01:062953 2309 003 090226
                            2020-01-25 00:17:34: 1: Relay_heat_demand --- i --- 02:023727 --:------ 02:023727 0008 002 fc00
                            2020-01-25 00:17:37: 1: Sync --- i --- 01:062953 --:------ 01:062953 1f09 003 ff0744
                            2020-01-25 00:17:37: 1: Setpoint_ctl --- i --- 01:062953 --:------ 01:062953 2309 036 0006810106410201f40304450406200505c80606ad0701f408 01f40902260a06400b01f4
                            2020-01-25 00:17:37: 1: Zone_temperature --- i --- 01:062953 --:------ 01:062953 30c9 036 0008700108660207bc0307bc04086605078a06076c0706b808 07220907350a076a0b06b8
                            2020-01-25 00:20:05: 1: Window_status --- i --- 04:160544 --:------ 01:062953 12b0 003 0a0000
                            2020-01-25 00:20:08: 1: Window_status --- i --- 04:160544 --:------ 01:062953 12b0 003 0a0000
                            2020-01-25 00:20:18: 1: Setpoint --- i --- 04:160544 --:------ 01:062953 2309 003 0a0640
                            2020-01-25 00:20:19: 1: Unknown command: --- i --- 03:125833 --:------ 03:125833 2389 003 02ffe0
                            2020-01-25 00:20:19: 1: --- i --- 03:125833 --:------ 03:125833 2389 003 02ffe0
                            2020-01-25 00:20:19: 1: External_sensor --- i --- 03:125833 --:------ 03:125833 0002 004 03020105
                            2020-01-25 00:20:43: 1: Sync --- i --- 01:062953 --:------ 01:062953 1f09 003 ff0744
                            2020-01-25 00:20:43: 1: Setpoint_ctl --- i --- 01:062953 --:------ 01:062953 2309 036 0006810106410201f40304450406200505c80606ad0701f408 01f40902260a06400b01f4
                            2020-01-25 00:20:43: 1: Zone_temperature --- i --- 01:062953 --:------ 01:062953 30c9 036 0008700108660207bc0307bc04086605078a06076c0706b808 07220907350a076a0b06b8
                            2020-01-25 00:21:13: 1: Zone_heat_demand --- i --- 04:160544 --:------ 01:062953 3150 002 0a00
                            2020-01-25 00:21:29: 1: Actuator_state --- i --- 13:233522 --:------ 13:233522 3ef0 003 0000ff
                            2020-01-25 00:21:29: 1: Actuator_check_req --- i --- 13:233522 --:------ 13:233522 3b00 002 00c8
                            2020-01-25 00:21:34: 1: Actuator_check_req --- i --- 01:062953 --:------ 01:062953 3b00 002 fcc8
                            2020-01-25 00:21:52: 1: Zone_temperature --- i --- 04:146232 --:------ 04:146232 30c9 003 00070d
                            2020-01-25 00:23:49: 1: Sync --- i --- 01:062953 --:------ 01:062953 1f09 003 ff0744
                            2020-01-25 00:23:49: 1: Setpoint_ctl --- i --- 01:062953 --:------ 01:062953 2309 036 0006810106410201f40304450406200505c80606ad0701f408 01f40902260a06400b01f4
                            2020-01-25 00:23:49: 1: Zone_temperature --- i --- 01:062953 --:------ 01:062953 30c9 036 0008700108660207bc0307bc04086605078a06076c0706b808 070d0907350a076a0b06b8
                            2020-01-25 00:24:37: 1: Unknown command: --- i --- 03:255832 --:------ 03:255832 2389 003 02fb64
                            2020-01-25 00:24:37: 1: --- i --- 03:255832 --:------ 03:255832 2389 003 02fb64
                            2020-01-25 00:24:37: 1: External_sensor --- i --- 03:255832 --:------ 03:255832 0002 004 03020105
                            2020-01-25 00:26:12: 1: Zone_temperature --- i --- 04:146262 --:------ 04:146262 30c9 003 000723
                            2020-01-25 00:26:29: 1: Actuator_state --- i --- 13:233522 --:------ 13:233522 3ef0 003 0000ff
                            2020-01-25 00:26:29: 1: --- i --- 13:233522 --:------ 13 :233522 3b00 002 00c8
                            2020-01-25 00:26:33: 1: Actuator_check_req --- i --- 01:062953 --:------ 01:062953 3b00 002 fcc8
                            2020-01-25 00:26:55: 1: Sync --- i --- 01:062953 --:------ 01:062953 1f09 003 ff0744
                            2020-01-25 00:26:55: 1: Setpoint_ctl --- i --- 01:062953 --:------ 01:062953 2309 036 0006810106410201f40304450406200505c80606ad0701f408 01f40902260a06400b01f4
                            2020-01-25 00:26:55: 1: Zone_temperature --- i --- 01:062953 --:------ 01:062953 30c9 036 0008700108660207a70307bc04086605078a06076c0706b808 070d0907230a076a0b06b8
                            2020-01-25 00:27:36: 1: Relay_heat_demand --- i --- 01:062953 --:------ 01:062953 0008 002 fc00
                            2020-01-25 00:30:01: 1: Sync --- i --- 01:062953 --:------ 01:062953 1f09 003 ff0744
                            2020-01-25 00:30:01: 1: Zone_info --- i --- 01:062953 --:------ 01:062953 000a 048 001401f40dac011401f40dac021001f40dac031401f40dac04 1401f40dac051401f40dac061401f40dac071401f40dac
                            2020-01-25 00:30:01: 1: Zone_info --- i --- 01:062953 --:------ 01:062953 000a 024 081001f40dac091001f40dac0a1001f40dac0b1401f40dac
                            2020-01-25 00:30:05: 1: Zone_temperature --- i --- 04:160544 --:------ 04:160544 30c9 003 000756
                            2020-01-25 00:30:23: 1: Relay_heat_demand --- i --- 02:025324 --:------ 02:025324 0008 002 fc00
                            2020-01-25 00:30:48: 1: External_sensor --- i --- 03:256140 --:------ 03:256140 0002 004 03020105
                            2020-01-25 00:31:29: 1: Actuator_state --- i --- 13:233522 --:------ 13:233522 3ef0 003 0000ff
                            2020-01-25 00:31:31: 1: Actuator_check_req --- i --- 01:062953 --:------ 01:062953 3b00 002 fcc8
                            2020-01-25 00:31:38: 1: Zone_heat_demand --- i --- 04:146232 --:------ 01:062953 3150 002 0800
                            2020-01-25 00:31:38: 1: Zone_heat_demand --- i --- 04:146262 --:------ 01:062953 3150 002 0900
                            2020-01-25 00:31:43: 1: Zone_heat_demand --- i --- 01:062953 --:------ 01:062953 3150 002 fc00
                            2020-01-25 00:32:14: 1: Zone_temperature --- i --- 04:146262 --:------ 04:146262 30c9 003 00070e
                            2020-01-25 00:32:34: 1: Relay_heat_demand --- i --- 02:023727 --:------ 02:023727 0008 002 fc00
                            2020-01-25 00:32:53: 1: Zone_temperature --- i --- 04:146232 --:------ 04:146232 30c9 003 0006fa
                            2020-01-25 00:33:07: 1: Sync --- i --- 01:062953 --:------ 01:062953 1f09 003 ff0744
                            2020-01-25 00:33:07: 1: Setpoint_ctl --- i --- 01:062953 --:------ 01:062953 2309 036 0006810106410201f40304450406200505c80606ad0701f408 01f40902260a06400b01f4
                            2020-01-25 00:33:07: 1: Zone_temperature --- i --- 01:062953 --:------ 01:062953 30c9 036 0008700108660207b10307bc04086605078a06076c0706b808 06fa09070e0a07560b06b8
                            2020-01-25 00:34:30: 1: Unknown command: --- i --- 03:256078 --:------ 03:256078 2389 003 02006f
                            2020-01-25 00:34:30: 1: --- i --- 03:256078 --:------ 03:256078 2389 003 02006f
                            2020-01-25 00:34:49: 1: Zone_temperature --- i --- 03:256140 --:------ 03:256140 30c9 003 01079e
                            2020-01-25 00:36:13: 1: Sync --- i --- 01:062953 --:------ 01:062953 1f09 003 ff0744
                            2020-01-25 00:36:13: 1: Setpoint_ctl --- i --- 01:062953 --:------ 01:062953 2309 036 0006810106410201f40304450406200505c80606af0701f408 01f40902260a06400b01f4
                            2020-01-25 00:36:13: 1: Zone_temperature --- i --- 01:062953 --:------ 01:062953 30c9 036 0008700108660207b10307bc04086605079e06076c0706b808 06fa09070e0a07560b06b8
                            2020-01-25 00:36:29: 1: --- i --- 13:233522 --:------ 13 :233522 3ef0 003 0000ff
                            2020-01-25 00:36:29: 1: Actuator_check_req --- i --- 13:233522 --:------ 13:233522 3b00 002 00c8
                            2020-01-25 00:36:32: 1: External_sensor --- i --- 03:256078 --:------ 03:256078 0002 004 03020105
                            2020-01-25 00:36:32: 1: Actuator_check_req --- i --- 01:062953 --:------ 01:062953 3b00 002 fcc8
                            2020-01-25 00:38:21: 1: External_sensor --- i --- 03:125827 --:------ 03:125827 0002 004 03020105
                            2020-01-25 00:39:04: 1: Zone_temperature --- i --- 04:160544 --:------ 04:160544 30c9 003 000741
                            2020-01-25 00:39:19: 1: Sync --- i --- 01:062953 --:------ 01:062953 1f09 003 ff0744
                            2020-01-25 00:39:19: 1: Setpoint_ctl --- i --- 01:062953 --:------ 01:062953 2309 036 0006810106410201f40304450406200505c80606af0701f408 01f40902260a06400b01f4
                            2020-01-25 00:39:19: 1: Zone_temperature --- i --- 01:062953 --:------ 01:062953 30c9 036 0008700108660207b10307bc04086605079e06076c0706b808 06fa09070e0a07410b06b8
                            2020-01-25 00:40:53: 1: Zone_temperature --- i --- 04:146232 --:------ 04:146232 30c9 003 0006e8
                            2020-01-25 00:41:16: 1: Zone_heat_demand --- i --- 04:160544 --:------ 01:062953 3150 002 0a00
                            2020-01-25 00:41:29: 1: Actuator_check_req --- i --- 13:233522 --:------ 13:233522 3b00 002 00c8
                            2020-01-25 00:41:29: 1: Actuator_check_req --- i --- 01:062953 --:------ 01:062953 3b00 002 fcc8
                            2020-01-25 00:42:25: 1: Sync --- i --- 01:062953 --:------ 01:062953 1f09 003 ff0744
                            2020-01-25 00:42:25: 1: Setpoint_ctl --- i --- 01:062953 --:------ 01:062953 2309 036 0006810106410201f40304450406200505c80606af0701f408 01f40902260a06400b01f4
                            2020-01-25 00:42:25: 1: Zone_temperature --- i --- 01:062953 --:------ 01:062953 30c9 036 0008700108660207b10307bc04086605079e06076c0706b808 06e809070e0a07410b06b8
                            2020-01-25 00:43:44: 1: Actuator_state --- rq --- 01:062953 13:233522 --:------ 3ef0 001 00
                            2020-01-25 00:43:46: 1: Actuator_state --- rq --- 01:062953 13:233522 --:------ 3ef0 001 00
                            2020-01-25 00:43:48: 1: Actuator_state --- rq --- 01:062953 13:233522 --:------ 3ef0 001 00
                            2020-01-25 00:45:13: 1: Zone_temperature --- i --- 04:146262 --:------ 04:146262 30c9 003 0006fb
                            2020-01-25 00:45:31: 1: Sync --- i --- 01:062953 --:------ 01:062953 1f09 003 ff0744
                            2020-01-25 00:45:31: 1: Setpoint_ctl --- i --- 01:062953 --:------ 01:062953 2309 036 0006810106410201f40304450406200505c80606af0701f408 01f40902260a06400b01f4
                            2020-01-25 00:45:31: 1: Zone_temperature --- i --- 01:062953 --:------ 01:062953 30c9 036 0008700108660207b10307bc04086605079e06076c0706b808 06e80906fb0a07410b06b8
                            2020-01-25 00:46:29: 1: Actuator_check_req --- i --- 13:233522 --:------ 13:233522 3b00 002 00c8
                            2020-01-25 00:46:29: 1: Actuator_state --- i --- 13:233522 --:------ 13:233522 3ef0 003 0000ff
                            2020-01-25 00:46:33: 1: Actuator_check_req --- i --- 01:062953 --:------ 01:062953 3b00 002 fcc8
                            2020-01-25 00:47:34: 1: Relay_heat_demand --- i --- 02:023727 --:------ 02:023727 0008 002 fc00
                            2020-01-25 00:47:40: 1: Relay_heat_demand --- i --- 01:062953 --:------ 01:062953 0008 002 fc00

                            Comment

                            • bruce_miranda
                              Automated Home Legend
                              • Jul 2014
                              • 2309

                              #29
                              Can you please show us evidence that the controller can show the heat demand from the individual zones of the UFH controller.

                              Comment

                              • smar
                                Automated Home Sr Member
                                • Feb 2018
                                • 57

                                #30
                                Originally posted by bruce_miranda View Post
                                Can you please show us evidence that the controller can show the heat demand from the individual zones of the UFH controller.
                                Here's a couple of lines (filtered out to show just the 02: messages):

                                Raw:
                                Code:
                                2020-01-26 08:26:21 |1| ZONE_HEAT_DEMAND   ---  I --- 02:043392 --:------ 02:043392 3150 006 00AC01BA029C
                                2020-01-26 08:41:21 |1| ZONE_HEAT_DEMAND   ---  I --- 02:043392 --:------ 01:139901 3150 002 0B9A
                                Decoded:
                                Code:
                                2020-01-26 08:26:21 |1| ZONE_HEAT_DEMAND    | I | UFH Controller        -> BROADCAST MESSAGE     |   86.0% @ Dining room          [Zone 8  ] 
                                2020-01-26 08:26:21 |1| ZONE_HEAT_DEMAND    | I | UFH Controller        -> BROADCAST MESSAGE     |   93.0% @ Kitchen UFH          [Zone 11 ] 
                                2020-01-26 08:26:21 |1| ZONE_HEAT_DEMAND    | I | UFH Controller        -> BROADCAST MESSAGE     |   78.0% @ Hallway              [Zone 12 ] 
                                2020-01-26 08:41:21 |1| ZONE_HEAT_DEMAND    | I | UFH Controller        -> CONTROLLER            |   77.0% @ Hallway              [Zone 12 ]

                                Comment

                                Working...
                                X