Thread: evohome HCE80 UFH valve state decoding from radio signals

  1. #11
    Automated Home Legend
    Join Date
    Jul 2014
    Posts
    2,307

    Default

    There are some 03: messages here that I have never seen before. Do you have an external temperature sensor on the older V2 Evohome?

    From your message, you appear to have 1 x Controller, 1 x BDR91 and then 2 more devices that I have never seen myself. i.e. the 03: devices 03:125829 and 03:255727

    Can you please describe your setup again? Or better still add a picture of your actual System Summary page on the controller, showing the various zone heat demands.

    P.S. : Re-read your previous notes on the other thread. My theory is that the 03: devices are your two HCW82.
    Last edited by bruce_miranda; 19th January 2020 at 04:06 PM.

  2. #12
    Automated Home Jr Member
    Join Date
    Dec 2019
    Posts
    21

    Default

    Yes, the 03 messages are from the two HCW82 temperature sensors. I checked the messages in-between adding each zone so we can be confident.
    FYI domoticz reports all zone temperatures fine. Although I don't know if it's getting them from the controller or from the 03 messages.

    The total setup is: 1 controller, 1 BDR91 to fire the boiler, 2 HCE80 (with 4 zones & 5 zones respectively; 8 UFH zones use HCW82 and the 9th uses the controller temperature) and 3 HR92 TRVs. So 12 zones in total. The 2 HCE80s share a single HRA80 antenna
    However, I wanted to run a simpler setup to try and understand UFH zone messages and the logs posted above are with just 3 zones working. The listener script devices.json describes this reduced system:

    {
    "01:062953": { "name" : "Study", "zoneId" : 1, "ufh_zoneId":2, "zoneMaster" : true },
    "30:071715": { "name" : "evoGateway", "zoneId" : 240, "zoneMaster" : false },
    "02:025324": { "name" : "HCE80_1", "zoneId" : -1, "zoneMaster" : false },
    "02:023727": { "name" : "HCE80_2", "zoneId" : -1, "zoneMaster" : false },
    "03:255727": { "name" : "Living room", "zoneId" : 2, "ufh_zoneId":0, "zoneMaster" : true },
    "03:125829": { "name" : "Garden room", "zoneId" : 3, "ufh_zoneID":1, "zoneMaster" : true },
    "13:233522": { "name" : "evoHeatDemand", "zoneId" : 252, "zoneMaster" : false }
    }

    Before setting it up I had factory reset controller & HCE80s and took the batteries out of unused HCW82s
    Hope that helps. Very happy to provide any more logs or try with other test configurations
    Last edited by Springgreens; 19th January 2020 at 04:40 PM.

  3. #13
    Automated Home Sr Member
    Join Date
    Feb 2018
    Posts
    57

    Default

    Here is a random 20 minutes of data from my system, filtered so that it is only showing the HCC80R messages:

    Code:
    2020-01-19 12:02:11 |1| RELAY_HEAT_DEMAND   | I | UFH Controller -> BROADCAST MESSAGE     |    0.0% @ UFH Controller                 
    2020-01-19 12:02:11 |1| UNKNOWN COMMAND     | I | UFH Controller -> BROADCAST MESSAGE     | Command code: 22D0, Payload: 00000002    
    2020-01-19 12:02:58 |2| ZONE_HEAT_DEMAND    | I | UFH Controller -> CONTROLLER            |   93.0% @ Kitchen UFH          [Zone 11] 
    2020-01-19 12:02:58 |1| ZONE_HEAT_DEMAND    | I | UFH Controller -> CONTROLLER            |   57.0% @ Hallway              [Zone 12] 
    2020-01-19 12:04:26 |1| ZONE_HEAT_DEMAND    | I | UFH Controller -> CONTROLLER            |   75.0% @ Dining room          [Zone 8 ] 
    2020-01-19 12:04:26 |1| ZONE_HEAT_DEMAND    | I | UFH Controller -> BROADCAST MESSAGE     |   75.0% @ Dining room          [Zone 8 ] 
    2020-01-19 12:04:26 |1| ZONE_HEAT_DEMAND    | I | UFH Controller -> BROADCAST MESSAGE     |   93.0% @ Kitchen UFH          [Zone 11] 
    2020-01-19 12:04:26 |1| ZONE_HEAT_DEMAND    | I | UFH Controller -> BROADCAST MESSAGE     |   57.0% @ Hallway              [Zone 12] 
    2020-01-19 12:06:57 |1| RELAY_HEAT_DEMAND   | I | UFH Controller -> BROADCAST MESSAGE     |    0.0% @ BDR Boiler Relay               
    2020-01-19 12:06:57 |1| ZONE_HEAT_DEMAND    | I | UFH Controller -> BROADCAST MESSAGE     |   93.0% @ Boiler Relay         [Zone 252] 
    2020-01-19 12:07:26 |1| ZONE_HEAT_DEMAND    | I | UFH Controller -> CONTROLLER            |   78.0% @ Dining room          [Zone 8 ] 
    2020-01-19 12:07:26 |1| ZONE_HEAT_DEMAND    | I | UFH Controller -> BROADCAST MESSAGE     |   78.0% @ Dining room          [Zone 8 ] 
    2020-01-19 12:07:26 |1| ZONE_HEAT_DEMAND    | I | UFH Controller -> BROADCAST MESSAGE     |   93.0% @ Kitchen UFH          [Zone 11] 
    2020-01-19 12:07:26 |1| ZONE_HEAT_DEMAND    | I | UFH Controller -> BROADCAST MESSAGE     |   57.0% @ Hallway              [Zone 12] 
    2020-01-19 12:08:05 |1| ZONE_HEAT_DEMAND    | I | UFH Controller -> BROADCAST MESSAGE     |   93.0% @ Boiler Relay         [Zone 252] 
    2020-01-19 12:10:26 |1| ZONE_HEAT_DEMAND    | I | UFH Controller -> BROADCAST MESSAGE     |   78.0% @ Dining room          [Zone 8 ] 
    2020-01-19 12:10:26 |1| ZONE_HEAT_DEMAND    | I | UFH Controller -> BROADCAST MESSAGE     |   93.0% @ Kitchen UFH          [Zone 11] 
    2020-01-19 12:10:26 |1| ZONE_HEAT_DEMAND    | I | UFH Controller -> BROADCAST MESSAGE     |   57.0% @ Hallway              [Zone 12] 
    2020-01-19 12:13:26 |1| ZONE_HEAT_DEMAND    | I | UFH Controller -> CONTROLLER            |   78.0% @ Dining room          [Zone 8 ] 
    2020-01-19 12:13:26 |1| ZONE_HEAT_DEMAND    | I | UFH Controller -> BROADCAST MESSAGE     |   78.0% @ Dining room          [Zone 8 ] 
    2020-01-19 12:13:26 |1| ZONE_HEAT_DEMAND    | I | UFH Controller -> BROADCAST MESSAGE     |   93.0% @ Kitchen UFH          [Zone 11] 
    2020-01-19 12:13:26 |1| ZONE_HEAT_DEMAND    | I | UFH Controller -> BROADCAST MESSAGE     |   57.0% @ Hallway              [Zone 12] 
    2020-01-19 12:18:10 |1| ZONE_HEAT_DEMAND    | I | UFH Controller -> CONTROLLER            |   78.0% @ Dining room          [Zone 8 ] 
    2020-01-19 12:18:10 |1| ZONE_HEAT_DEMAND    | I | UFH Controller -> CONTROLLER            |   57.0% @ Hallway              [Zone 12] 
    2020-01-19 12:19:07 |1| RELAY_HEAT_DEMAND   | I | UFH Controller -> BROADCAST MESSAGE     |    0.0% @ BDR Boiler Relay               
    2020-01-19 12:19:07 |1| ZONE_HEAT_DEMAND    | I | UFH Controller -> BROADCAST MESSAGE     |   93.0% @ Boiler Relay         [Zone 252] 
    2020-01-19 12:19:26 |1| ZONE_HEAT_DEMAND    | I | UFH Controller -> CONTROLLER            |   80.0% @ Dining room          [Zone 8 ] 
    2020-01-19 12:20:05 |1| RELAY_HEAT_DEMAND   | I | UFH Controller -> BROADCAST MESSAGE     |  100.0% @ BDR Boiler Relay               
    2020-01-19 12:20:05 |1| ZONE_HEAT_DEMAND    | I | UFH Controller -> BROADCAST MESSAGE     |   93.0% @ Boiler Relay         [Zone 252] 
    2020-01-19 12:22:26 |1| ZONE_HEAT_DEMAND    | I | UFH Controller -> BROADCAST MESSAGE     |   83.0% @ Dining room          [Zone 8 ]
    And the corresponding raw messages (different line counts as some of the raw messages contain multiple zones in one message):

    Code:
    2020-01-19 12:02:11 |1| RELAY_HEAT_DEMAND  ---  I --- 02:043392 --:------ 02:043392 0008 002 FA00
    2020-01-19 12:02:11 |1|                    ---  I --- 02:043392 --:------ 02:043392 22D0 004 00000002
    2020-01-19 12:02:58 |2| ZONE_HEAT_DEMAND   ---  I --- 02:043392 --:------ 01:139901 3150 002 0ABA
    2020-01-19 12:02:58 |1| ZONE_HEAT_DEMAND   ---  I --- 02:043392 --:------ 01:139901 3150 002 0B72
    2020-01-19 12:04:26 |1| ZONE_HEAT_DEMAND   ---  I --- 02:043392 --:------ 01:139901 3150 002 0796
    2020-01-19 12:04:26 |1| ZONE_HEAT_DEMAND   ---  I --- 02:043392 --:------ 02:043392 3150 006 009601BA0272
    2020-01-19 12:06:57 |1| RELAY_HEAT_DEMAND  ---  I --- 02:043392 --:------ 02:043392 0008 002 FC00
    2020-01-19 12:06:57 |1| ZONE_HEAT_DEMAND   ---  I --- 02:043392 --:------ 02:043392 3150 002 FCBA
    2020-01-19 12:07:26 |1| ZONE_HEAT_DEMAND   ---  I --- 02:043392 --:------ 01:139901 3150 002 079C
    2020-01-19 12:07:26 |1| ZONE_HEAT_DEMAND   ---  I --- 02:043392 --:------ 02:043392 3150 006 009C01BA0272
    2020-01-19 12:08:05 |1| ZONE_HEAT_DEMAND   ---  I --- 02:043392 --:------ 02:043392 3150 002 FCBA
    2020-01-19 12:10:26 |1| ZONE_HEAT_DEMAND   ---  I --- 02:043392 --:------ 02:043392 3150 006 009C01BA0272
    2020-01-19 12:13:26 |1| ZONE_HEAT_DEMAND   ---  I --- 02:043392 --:------ 01:139901 3150 002 079C
    2020-01-19 12:13:26 |1| ZONE_HEAT_DEMAND   ---  I --- 02:043392 --:------ 02:043392 3150 006 009C01BA0272
    2020-01-19 12:18:10 |1| ZONE_HEAT_DEMAND   ---  I --- 02:043392 --:------ 01:139901 3150 002 079C
    2020-01-19 12:18:10 |1|                    ---  I --- 02:043392 --:------ 01:139901 3150 002 	*ERR_BAD_STOP_BIT*
    2020-01-19 12:18:10 |1| ZONE_HEAT_DEMAND   ---  I --- 02:043392 --:------ 01:139901 3150 002 0B72
    2020-01-19 12:19:07 |1| RELAY_HEAT_DEMAND  ---  I --- 02:043392 --:------ 02:043392 0008 002 FC00
    2020-01-19 12:19:07 |1| ZONE_HEAT_DEMAND   ---  I --- 02:043392 --:------ 02:043392 3150 002 FCBA
    2020-01-19 12:19:26 |1| ZONE_HEAT_DEMAND   ---  I --- 02:043392 --:------ 01:139901 3150 002 07A0
    2020-01-19 12:20:05 |1| RELAY_HEAT_DEMAND  ---  I --- 02:043392 --:------ 02:043392 0008 002 FCC8
    2020-01-19 12:20:05 |1| ZONE_HEAT_DEMAND   ---  I --- 02:043392 --:------ 02:043392 3150 002 FCBA
    2020-01-19 12:22:26 |1| ZONE_HEAT_DEMAND   ---  I --- 02:043392 --:------ 02:043392 3150 006 00A601B80272
    Last edited by smar; 19th January 2020 at 07:09 PM.

  4. #14
    Automated Home Legend
    Join Date
    Jul 2014
    Posts
    2,307

    Default

    Quote Originally Posted by Springgreens View Post
    Yes, the 03 messages are from the two HCW82 temperature sensors. I checked the messages in-between adding each zone so we can be confident.
    FYI domoticz reports all zone temperatures fine. Although I don't know if it's getting them from the controller or from the 03 messages.

    The total setup is: 1 controller, 1 BDR91 to fire the boiler, 2 HCE80 (with 4 zones & 5 zones respectively; 8 UFH zones use HCW82 and the 9th uses the controller temperature) and 3 HR92 TRVs. So 12 zones in total. The 2 HCE80s share a single HRA80 antenna
    However, I wanted to run a simpler setup to try and understand UFH zone messages and the logs posted above are with just 3 zones working. The listener script devices.json describes this reduced system:

    {
    "01:062953": { "name" : "Study", "zoneId" : 1, "ufh_zoneId":2, "zoneMaster" : true },
    "30:071715": { "name" : "evoGateway", "zoneId" : 240, "zoneMaster" : false },
    "02:025324": { "name" : "HCE80_1", "zoneId" : -1, "zoneMaster" : false },
    "02:023727": { "name" : "HCE80_2", "zoneId" : -1, "zoneMaster" : false },
    "03:255727": { "name" : "Living room", "zoneId" : 2, "ufh_zoneId":0, "zoneMaster" : true },
    "03:125829": { "name" : "Garden room", "zoneId" : 3, "ufh_zoneID":1, "zoneMaster" : true },
    "13:233522": { "name" : "evoHeatDemand", "zoneId" : 252, "zoneMaster" : false }
    }

    Before setting it up I had factory reset controller & HCE80s and took the batteries out of unused HCW82s
    Hope that helps. Very happy to provide any more logs or try with other test configurations
    I would really like to see the System Summary screen on your Evohome controller.

  5. #15
    Automated Home Jr Member
    Join Date
    Dec 2019
    Posts
    21

    Default

    Here's a screenshot. It has the other zones back in now as I needed to have the heating working again over the week.

    systemSummary.jpg

    One odd thing is that the only non-zero values are for the boiler and the first zone on each of the two HCE80s (living room is zone1 #1 & Hall is zone1 on #2) but some of the other zones have green light on their HCE80. Hadn't noticed that before but it sounds close to what DanD was saying about difference between HCE80 & HCC80: that the HCE bundles the individual zone valve commands, or possibly doesn't send them at all
    I'm away a bit this week so will most likely not be able to experiment more until the weekend.

    Oh, and sorry but I don'y know anyone with the HGI80.
    Last edited by Springgreens; 19th January 2020 at 09:13 PM.

  6. #16
    Automated Home Legend
    Join Date
    Jul 2014
    Posts
    2,307

    Default

    The weird thing is that there were absolutely NO messages from your UFH controller in the dump that you added earlier. I don't know over what time period that dump was taken but I would have expected atleast some messages from the 02: devices if the HCE80 is indeed an 02: device like the HCC80R. It doesn't matter if you added more zones now, what would be good is to have ALL raw radio messages captured for about 4 hours. Put it in the file and upload that file somewhere so Dan and I can have a look at it. Your installation is quite interesting as a case study. We don't see many HCE80s.
    I actually think the HCE80 is summing up the Heat Demand for the entire controller and sending it to the Evohome as a single Heat Demand single. And this is exactly why I have been asking to see the System Summary page for your controller. Because if that page cannot show the individual zone Heat Demands, then there is no way we can. I have been able to find everything else in your dump i.e. zone temps, set points, upper and lower maxs etc. But not the individual heat demands.

    P.S. Relooked at the other thread. You defined 30:071715": { "name" : "evoGateway", "zoneId" : 240, "zoneMaster" : false} Why ? You have the V3 of the controller which doesn't need an Internet Gateway.
    Last edited by bruce_miranda; 19th January 2020 at 09:32 PM.

  7. #17
    Automated Home Jr Member
    Join Date
    Dec 2019
    Posts
    21

    Default

    Yes, I see what you mean. Actually it ran all night and I just looked at the log file - same as extract above there are no 02: messages at all.
    I definitialy had some earlier. Have switched back to the ghoti57/master branch firmware and will set a recording going again later. I'm away tomorroy and back quite late Tuesday so may be wednesday evening before I can get the results to you.

  8. #18
    Automated Home Sr Member
    Join Date
    Feb 2018
    Posts
    57

    Default

    Quote Originally Posted by Springgreens View Post
    Yes, I see what you mean. Actually it ran all night and I just looked at the log file - same as extract above there are no 02: messages at all.
    I definitialy had some earlier. Have switched back to the ghoti57/master branch firmware and will set a recording going again later. I'm away tomorroy and back quite late Tuesday so may be wednesday evening before I can get the results to you.
    I recall when I was testing with one of ghoti's firmwares (I think the master) I wasn't receiving any messages from my HCC80R. Switching to the other fifo branch, the messages immediately started coming through (or possibly the other way round!).

  9. #19
    Automated Home Sr Member
    Join Date
    Feb 2018
    Posts
    57

    Default

    Quote Originally Posted by bruce_miranda View Post

    P.S. Relooked at the other thread. You defined 30:071715": { "name" : "evoGateway", "zoneId" : 240, "zoneMaster" : false} Why ? You have the V3 of the controller which doesn't need an Internet Gateway.
    That's actually the way I've done the script - when sending messages, it sends it from that 30: id, so that the evohome controller thinks it is getting a valid instruction from an internet gateway.

  10. #20
    Automated Home Jr Member
    Join Date
    Dec 2019
    Posts
    21

    Default

    Here's a log I had from a few days over last week. Recorded with smar's listener python & ghoti57 master branch firmware.
    I gave up trying to upload either zip or txt. Here's messages filtered for '- 02:'
    I guess all too short to contain individual zone info?

    ther's repeated messages below just becasue of the way notepad++ search works - check the line numbers

    Line 506: 2020-01-16 03:22:43: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FC00
    Line 507: 2020-01-16 03:24:09: 1: --- I --- 02:023727 *ERR_BAD_STOP_BIT*
    Line 517: 2020-01-16 03:31:19: 1: --- I --- 02:025324 --:------ 02:025324 *ERR_BAD_STOP_BIT*
    Line 517: 2020-01-16 03:31:19: 1: --- I --- 02:025324 --:------ 02:025324 *ERR_BAD_STOP_BIT*
    Line 526: 2020-01-16 03:34:43: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FC00
    Line 526: 2020-01-16 03:34:43: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FC00
    Line 527: 2020-01-16 03:36:13: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FC00
    Line 527: 2020-01-16 03:36:13: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FC00
    Line 530: 2020-01-16 03:38:55: 1: ZONE_HEAT_DEMAND --- I --- 02:023727 --:------ 01:062953 3150 002 0364
    Line 536: 2020-01-16 03:43:19: 1: --- I --- 02:025324 --:------ *ERR_BAD_STOP_BIT*
    Line 540: 2020-01-16 03:43:59: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FCC8
    Line 540: 2020-01-16 03:43:59: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FCC8
    Line 545: 2020-01-16 03:48:16: 1: --- I --- 02:023727 --:------ 02:023727 *ERR_BAD_STOP_BIT*
    Line 545: 2020-01-16 03:48:16: 1: --- I --- 02:023727 --:------ 02:023727 *ERR_BAD_STOP_BIT*
    Line 556: 2020-01-16 03:53:54: 1: --- I --- 02:023727 --:------ *ERR_BAD_STOP_BIT*
    Line 558: 2020-01-16 03:55:19: 1: --- I --- 02:025324 --:------ 02:025324 0008 002 FCC8 *ERR_BAD_STOP_BIT*
    Line 558: 2020-01-16 03:55:19: 1: --- I --- 02:025324 --:------ 02:025324 0008 002 FCC8 *ERR_BAD_STOP_BIT*
    Line 559: 2020-01-16 03:56:03: 1: --- I --- 02:023727 *ERR_BAD_STOP_BIT*
    Line 566: 2020-01-16 04:00:20: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FC00
    Line 566: 2020-01-16 04:00:20: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FC00
    Line 586: 2020-01-16 04:08:07: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FCC8
    Line 586: 2020-01-16 04:08:07: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FCC8
    Line 590: 2020-01-16 04:08:54: 1: ZONE_HEAT_DEMAND --- I --- 02:023727 --:------ 01:062953 3150 002 0364
    Line 591: 2020-01-16 04:10:42: 1: --- I --- 02:025324 --:------ 02:025324 *ERR_BAD_STOP_BIT*
    Line 591: 2020-01-16 04:10:42: 1: --- I --- 02:025324 --:------ 02:025324 *ERR_BAD_STOP_BIT*
    Line 599: 2020-01-16 04:12:24: 1: --- I --- 02:023727 --:------ *ERR_BAD_STOP_BIT*
    Line 607: 2020-01-16 04:20:11: 1: --- I --- 02:023727 --:------ *ERR_BAD_STOP_BIT*
    Line 615: 2020-01-16 04:23:54: 1: --- I --- 02:023727 --:------ 01:062953 3150 002 03 *ERR_BAD_STOP_BIT*
    Line 619: 2020-01-16 04:24:28: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FC00
    Line 619: 2020-01-16 04:24:28: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FC00
    Line 629: 2020-01-16 04:31:18: 1: --- I --- 02:025324 --:------ 02:025324 0008 002 FCC8 *ERR_BAD_STOP_BIT*
    Line 629: 2020-01-16 04:31:18: 1: --- I --- 02:025324 --:------ 02:025324 0008 002 FCC8 *ERR_BAD_STOP_BIT*
    Line 631: 2020-01-16 04:32:15: 1: --- I --- 02:023727 --:------ *ERR_BAD_STOP_BIT*
    Line 640: 2020-01-16 04:38:54: 1: ZONE_HEAT_DEMAND --- I --- 02:023727 --:------ 01:062953 3150 002 0364
    Line 649: 2020-01-16 04:43:18: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FCC8
    Line 649: 2020-01-16 04:43:18: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FCC8
    Line 650: 2020-01-16 04:44:19: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FCC8
    Line 650: 2020-01-16 04:44:19: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FCC8
    Line 654: 2020-01-16 04:46:42: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FC00
    Line 654: 2020-01-16 04:46:42: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FC00
    Line 665: 2020-01-16 04:53:54: 1: --- I --- 02:023727 --:------ *ERR_BAD_STOP_BIT*
    Line 670: 2020-01-16 04:55:18: 1: --- I --- 02:025324 --:------ 02:025324 *ERR_BAD_STOP_BIT*
    Line 670: 2020-01-16 04:55:18: 1: --- I --- 02:025324 --:------ 02:025324 *ERR_BAD_STOP_BIT*
    Line 679: 2020-01-16 05:00:40: 1: --- I --- 02:023727 --:------ 02:023727 *ERR_BAD_STOP_BIT*
    Line 679: 2020-01-16 05:00:40: 1: --- I --- 02:023727 --:------ 02:023727 *ERR_BAD_STOP_BIT*
    Line 696: 2020-01-16 05:07:18: 1: --- I --- 02:025324 --:------ 02:025324 *ERR_BAD_STOP_BIT*
    Line 696: 2020-01-16 05:07:18: 1: --- I --- 02:025324 --:------ 02:025324 *ERR_BAD_STOP_BIT*
    Line 700: 2020-01-16 05:08:27: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FCC8
    Line 700: 2020-01-16 05:08:27: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FCC8
    Line 701: 2020-01-16 05:08:54: 1: ZONE_HEAT_DEMAND --- I --- 02:023727 --:------ 01:062953 3150 002 0364
    Line 705: 2020-01-16 05:10:42: 1: --- I --- 02:025324 --:------ 02:025324 *ERR_BAD_STOP_BIT*
    Line 705: 2020-01-16 05:10:42: 1: --- I --- 02:025324 --:------ 02:025324 *ERR_BAD_STOP_BIT*
    Line 710: 2020-01-16 05:12:44: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FC00
    Line 710: 2020-01-16 05:12:44: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FC00
    Line 718: 2020-01-16 05:19:18: 1: --- I --- 02:025324 --:------ *ERR_BAD_STOP_BIT*
    Line 725: 2020-01-16 05:22:42: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FC00
    Line 725: 2020-01-16 05:22:42: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FC00
    Line 729: 2020-01-16 05:24:48: 1: --- I --- 02:023727 --:------ 02:023727 0008 002 FC *ERR_BAD_STOP_BIT*
    Line 729: 2020-01-16 05:24:48: 1: --- I --- 02:023727 --:------ 02:023727 0008 002 FC *ERR_BAD_STOP_BIT*
    Line 739: 2020-01-16 05:31:18: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FCC8
    Line 739: 2020-01-16 05:31:18: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FCC8
    Line 744: 2020-01-16 05:32:35: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FCC8
    Line 744: 2020-01-16 05:32:35: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FCC8
    Line 746: 2020-01-16 05:34:42: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FC00
    Line 746: 2020-01-16 05:34:42: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FC00
    Line 750: 2020-01-16 05:36:52: 1: --- I --- 02:023727 --:------ 02:023727 *ERR_BAD_STOP_BIT*
    Line 750: 2020-01-16 05:36:52: 1: --- I --- 02:023727 --:------ 02:023727 *ERR_BAD_STOP_BIT*
    Line 754: 2020-01-16 05:38:53: 1: --- I --- 02:023727 --:------ *ERR_BAD_STOP_BIT*
    Line 760: 2020-01-16 05:43:18: 1: --- I --- 02:025324 --:------ 02:025324 *ERR_BAD_STOP_BIT*
    Line 760: 2020-01-16 05:43:18: 1: --- I --- 02:025324 --:------ 02:025324 *ERR_BAD_STOP_BIT*
    Line 761: 2020-01-16 05:44:38: 1: --- I --- 02:023727 --:------ *ERR_BAD_STOP_BIT*
    Line 765: 2020-01-16 05:46:42: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FC00
    Line 765: 2020-01-16 05:46:42: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FC00
    Line 776: 2020-01-16 05:53:53: 1: --- I --- 02:023727 --:------ 01:062953 3150 002 0364 *ERR_BAD_STOP_BIT*
    Line 781: 2020-01-16 05:55:18: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FCC8
    Line 781: 2020-01-16 05:55:18: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FCC8
    Line 782: 2020-01-16 05:56:42: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FCC8
    Line 782: 2020-01-16 05:56:42: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FCC8
    Line 786: 2020-01-16 05:58:42: 1: --- I --- 02:025324 --:------ 02:025324 0008 002 FC *ERR_BAD_STOP_BIT*
    Line 786: 2020-01-16 05:58:42: 1: --- I --- 02:025324 --:------ 02:025324 0008 002 FC *ERR_BAD_STOP_BIT*
    Line 796: 2020-01-16 06:00:59: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FC00
    Line 796: 2020-01-16 06:00:59: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FC00
    Line 811: 2020-01-16 06:07:17: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FCC8
    Line 811: 2020-01-16 06:07:17: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FCC8
    Line 813: 2020-01-16 06:08:53: 1: ZONE_HEAT_DEMAND --- I --- 02:023727 --:------ 01:062953 3150 002 0364
    Line 824: 2020-01-16 06:13:03: 1: --- I --- 02:023727 --:------ 02:023727 *ERR_BAD_STOP_BIT*
    Line 824: 2020-01-16 06:13:03: 1: --- I --- 02:023727 --:------ 02:023727 *ERR_BAD_STOP_BIT*
    Line 832: 2020-01-16 06:19:17: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FCC8
    Line 832: 2020-01-16 06:19:17: 1: RELAY_HEAT_DEMAND --- I --- 02:025324 --:------ 02:025324 0008 002 FCC8
    Line 833: 2020-01-16 06:20:50: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FCC8
    Line 833: 2020-01-16 06:20:50: 1: RELAY_HEAT_DEMAND --- I --- 02:023727 --:------ 02:023727 0008 002 FCC8