    Default Heat Sink Radiator

    Hi
    I have an 8 Rad system....7 with Evohome HR92’s on and one rad in bathroom acting as a heat sink ( lock shield valves ) all working fine.....not sure i should have said that anyway I understand need for heat sink rad on system that just has thermostatic valves in case all close and boiler is still running but on evohome if all HR92’s are shut then boiler shouldn’t run so could I add HR92 to the bathroom rad which is acting as the heat sink rad

    Hot water is heated from a separate instant water heater.

    Many thanks in advance

    Mick

  2. #2
    Automated Home Jr Member
    Join Date
    Aug 2019
    Posts
    30

    Default

    i had a new system installed last year,initially the plumbers planed to install my bathroom radiator exactly as you describe.

    I explained I wanted HR92s on all radiators (10),which was easily achieved by installing a by pass valve,this was installed in my loft along with the boiler.

    I guess you need the same,however I am not a plumber ,Im sure someone else will clarify or correct if I'm wrong

    I like you have water heated via immersion heater.
    Last edited by anniesboy; 18th September 2020 at 05:46 PM.

  3. #3
    Automated Home Sr Member
    Join Date
    Apr 2016
    Posts
    61

    Default

    I have HR92s on all radiators and my boiler includes an ABV. The system has been working without problems for 6 years. Fitting an external ABV might be necessary depending on your boiler but should not be difficult to install.

  4. #4
    Automated Home Sr Member
    Join Date
    Oct 2017
    Posts
    75

    Default

    Quote Originally Posted by Mickjohn View Post
    Hi
    .... I understand need for heat sink rad on system that just has thermostatic valves in case all close and boiler is still running but on evohome if all HR92’s are shut then boiler shouldn’t run so could I add HR92 to the bathroom rad which is acting as the heat sink rad
    Mick
    I have the same question. Why would the pump or boiler run when the valves are all shut? Especially an old fashioned system like mine (Ideal Mexico, no fancy controls). I just can’t understand why any sort of bypass would be needed.

  5. #5
    Automated Home Jr Member
    Join Date
    Mar 2015
    Posts
    48

    Default

    Quote Originally Posted by anniesboy View Post
    i had a new system installed last year,initially the plumbers planed to install my bathroom radiator exactly as you describe.

    I explained I wanted HR92s on all radiators (10),which was easily achieved by installing a by pass valve,this was installed in my loft along with the boiler.

    I guess you need the same,however I am not a plumber ,Im sure someone else will clarify or correct if I'm wrong

    I like you have water heated via immersion heater.
    Thank you for reply seems by pass valve will be the way to go btw i have instant water heater not emersion heater

    Mick

  6. #6
    Automated Home Jr Member
    Join Date
    Aug 2019
    Posts
    30

    Default

    Here is a link to why a bypass is installed.
    https://www.youtube.com/watch?v=7sp78lBoSPw&t=93s

  7. #7
    Automated Home Jr Member
    Join Date
    Aug 2018
    Posts
    36

    Default

    I'd be thoughtful about that. My boiler apparently has an ABV but, as belt and braces, I use a large towel rad as a bypass in case of pump overruns.
    The bonus is that towels are always bone dry.

  8. #8
    Automated Home Jr Member
    Join Date
    Mar 2015
    Posts
    48

    Default

    Thank you for the above replies much appreciated but instead of ripping up floor boards to fit an automatic bypass valve what about setting a custom schedule at set point say 5 degrees add all present HR92's ( in summer) and install a single zone thermostat (Y87RF) in bathroom and bound to my evohome controller.
    Wouldnt that effectivley control the bathroom rad? or am I missing something?

    Many thanks in advance

    Mick

  9. #9
    Automated Home Legend
    Join Date
    Sep 2014
    Location
    Scotland
    Posts
    2,098

    Default

    I don't understand why you would need to rip up your floor boards to install an automatic bypass valve. They're usually installed within about a metre of the boiler so unless you have a very short pipe run from the boiler before the pipes disappear into the floor installing an ABV shouldn't be a problem.
    Last edited by DBMandrake; 23rd September 2020 at 09:20 PM.

  10. #10
    Automated Home Legend
    Join Date
    Sep 2014
    Location
    Scotland
    Posts
    2,098

    Default

    Quote Originally Posted by filbert View Post
    I have the same question. Why would the pump or boiler run when the valves are all shut? Especially an old fashioned system like mine (Ideal Mexico, no fancy controls). I just can’t understand why any sort of bypass would be needed.
    Most boilers have pump overrun so when the boiler demand signal is turned off (BDR91 etc) the pump will continue to run for a few minutes. If all the valves are closed and there is nowhere for that overrun to flow the pump will not be very happy trying to pump into a dead end...

    Also you can't trust the Evohome system to never allow the boiler relay to turn on when all HR92's are closed and blocking water flow - it actually happens in certain normal circumstances (for short periods of time) let alone if there is any intermittent wireless comms which could let it happen for a long period of time.

    If you want all radiators controlled in an Evohome system you need an automatic bypass. Personally I think it's worth it and I had an automatic bypass installed so I could control all radiators on our system.
    Last edited by DBMandrake; 23rd September 2020 at 09:23 PM.