Page 14 of 87 FirstFirst ... 49101112131415161718192464 ... LastLast
Results 131 to 140 of 870

Thread: Evohome firmware 02.00.19.31 Beta Trial - Exclusive for Automated Home Members

  1. #131
    Automated Home Guru
    Join Date
    Sep 2018
    Location
    Scotland
    Posts
    214

    Default

    I see Warm Weather Saver in action. I have one zone demanding 4% and the other 8% but with outdoor temperature of 10C the boiler pump is not running.

    Previously it would be in overrun.

  2. #132
    Automated Home Legend
    Join Date
    Jul 2014
    Posts
    1,677

    Default

    Anyone with an OTGW should be able to confirm this pretty easily. Just check for any OT commands referring to the Outside temperature being passed between the OTB and the boiler. Then just switch the home wifi off and see what the controller does before a Cold Boost zone switches on. Is it able to boost or ignores the boost.

  3. #133
    Automated Home Sr Member
    Join Date
    Apr 2019
    Posts
    63

    Default Cold Weather Boost Suggestion

    This cold weather boost needs some work.

    I have sketched suggestion how I think it should work which would work good if possible, and allow user to calibrate to there house and there individual room if possible.

    I definitely need a different SP differential, this morning I was boost and house was warm, very sunny outside but 9'C on evo touch screen. - 12 would be good to start boost at 0.5'C then we should have 2nd differential, lets say -18, then I would want to boost 2'C. The boost should be proportionally scaled between these to set points.


    There should be 2 differential's and 2 boost SP's
    The Differential SP's should be variable.
    The boost SP's should be proportional to differential.

    This would be awesome if possible and if could be done by individual room

    Cold Weather Boost Suggestion.jpg
    Last edited by frankmalia; 5th April 2020 at 01:03 PM.

  4. #134
    Automated Home Guru
    Join Date
    Dec 2012
    Posts
    172

    Default

    Quote Originally Posted by kevinsmart View Post
    I see Warm Weather Saver in action. I have one zone demanding 4% and the other 8% but with outdoor temperature of 10C the boiler pump is not running.

    Previously it would be in overrun.
    is there an easy way to spot its operating? I've switched off eco mode and immediately the rooms show as needing heat according to the main panel. Is the only way to spot its operational is to monitor the installer menu>boiler demand screen? Im a programmer and data architect and I am not a fan of "hidden features" as users always wonder if the "feature" is really working or not

  5. #135
    Automated Home Legend paulockenden's Avatar
    Join Date
    Apr 2015
    Location
    South Coast
    Posts
    1,719

    Default

    I'm sure the email said there's new icons...

  6. #136
    Automated Home Legend
    Join Date
    Sep 2014
    Location
    Scotland
    Posts
    2,349

    Default

    Quote Originally Posted by SteveP View Post
    re-enabled cold weather cold weather boost and Advanced Load Scaling yesterday (still have warm weather saver enable). Glorious sunshine today and house is like an oven this morning - how come as warm weather saver should have kicked in? Outside temp in the shade as read by my weather station is 14.2C Evohome showing temp as 9C !! This will be the downside as ideally evohome should support a remote temp sensor so it gets the local true temp not a remote generalised internet temp Nice idea though but once again have had to manually enable eco mode
    Keep in mind that there is typically a lag - sometimes of a few hours between actual temperature at your location and the temperature reported by most online weather services. I use weather.com data for another project and typically see a lag of 1-3 hours versus my actual outdoor weather station. I also see similar on the evohome reported temperature which typically lags behind significantly.

    It seems that rather than using the temperature forecast earlier in the day for "now", (which would give zero lag but rely on the prediction being accurate) they use the last known temperature measurement which can be a few hours out of date as they don't update in realtime.

    So on a day where temperature is rising rapidly you'll see the internet reported figure which is lagging behind being too low, and in the evening during a rapid cool down the internet reported figure will typically be too high.

    Another thing to keep in mind is the geographical resolution of different weather services which varies a lot from one service to another. Just because you have your location entered correctly in the TCC portal doesn't mean the weather service Honeywell uses has observation stations near your location. For example I live in Motherwell and while weather.com lets you use Motherwell as a location the data it returns is identical to the data for Glasgow - which is 17 miles away and has quite different temperatures and weather patterns due to the heat island effect. (And probably also affected by the Clyde river)

    I don't know which weather service Evohome is using (has anyone figured it out ?) but it may be that you're simply a long way from the nearest weather station that service uses so you're getting weather for a nearby town or an extrapolation from further away weather stations.

    In my location the Evohome doesn't do too badly - there is a bit of lag but it's usually within a couple of degrees most of the day so accurate enough for weather compensation. Right now my weather station reports 17.7 degrees - which has risen a degree in the last 30 minutes thanks to clouds finally breaking, and the Evotouch is reporting 15C which it has done for at least the last couple of hours.

    No internet weather service will give the same accuracy as an on-site, properly located and installed weather station/sensor, but super high accuracy is not needed for weather compensation.
    Last edited by DBMandrake; 5th April 2020 at 03:23 PM.

  7. #137
    Automated Home Legend
    Join Date
    Sep 2014
    Location
    Scotland
    Posts
    2,349

    Default

    Quote Originally Posted by kevinsmart View Post
    I see Warm Weather Saver in action. I have one zone demanding 4% and the other 8% but with outdoor temperature of 10C the boiler pump is not running.

    Previously it would be in overrun.
    Are you sure that's new ? Is your system TPI or OpenTherm ?

    Because on a TPI system with the default 6 cycles an hour and 1 minute on time the boiler won't fire until there is at least 10% heat demand.

  8. #138
    Automated Home Guru
    Join Date
    Dec 2012
    Posts
    172

    Default

    Quote Originally Posted by DBMandrake View Post
    Keep in mind that there is typically a lag - sometimes of a few hours between actual temperature at your location and the temperature reported by most online weather services. I use weather.com data for another project and typically see a lag of 1-3 hours versus my actual outdoor weather station. I also see similar on the evohome reported temperature which typically lags behind significantly.

    It seems that rather than using the temperature forecast earlier in the day for "now", (which would give zero lag but rely on the prediction being accurate) they use the last known temperature measurement which can be a few hours out of date as they don't update in realtime.

    So on a day where temperature is rising rapidly you'll see the internet reported figure which is lagging behind being too low, and in the evening during a rapid cool down the internet reported figure will typically be too high.

    Another thing to keep in mind is the geographical resolution of different weather services which varies a lot from one service to another. Just because you have your location entered correctly in the TCC portal doesn't mean the weather service Honeywell uses has observation stations near your location. For example I live in Motherwell and while weather.com lets you use Motherwell as a location the data it returns is identical to the data for Glasgow - which is 17 miles away and has quite different temperatures and weather patterns due to the heat island effect. (And probably also affected by the Clyde river)

    I don't know which weather service Evohome is using (has anyone figured it out ?) but it may be that you're simply a long way from the nearest weather station that service uses so you're getting weather for a nearby town or an extrapolation from further away weather stations.

    In my location the Evohome doesn't do too badly - there is a bit of lag but it's usually within a couple of degrees most of the day so accurate enough for weather compensation. Right now my weather station reports 17.7 degrees - which has risen a degree in the last 30 minutes thanks to clouds finally breaking, and the Evotouch is reporting 15C which it has done for at least the last couple of hours.

    No internet weather service will give the same accuracy as an on-site, properly located and installed weather station/sensor, but super high accuracy is not needed for weather compensation.
    Yep agree with all your observations and that there is a high dependency as to where the local weather station is plus each evohome owners physical location and surrounding. We are protected by hills from northerly winds but this morning we have southerlies so nicely warming up the house the issue really is that when you hit the boundary of the cold boost in terms of the actual outside temperature (14.5c) vs the evohome reported outside temp (9C) the difference is enough to be boosting the heating rather than setting it back. That will always be an issue with using internet weather data. Would be useful to know what weather data is being used by evohome as may help identify the accuracy? What may be an option that doesn't involve physically changing the evohome electronics would be to link a DT92 as an outside temp stat and use a zone to record the outside temp until a water proof outside temp stat is available? The DT92 needs to be mounted in a waterproof box but I would gladly give up a zone for better outside temperature compensation as my boiler is a trusty Valliant Combi that I have been told has many more years life and so I wont be able to justify to "the boss" changing the boiler for some time just so I can enjoy opentherm benefits

  9. #139
    Automated Home Guru
    Join Date
    Dec 2012
    Posts
    172

    Default

    Quote Originally Posted by paulockenden View Post
    I'm sure the email said there's new icons...
    Paul, from the email I can only see cold boost icons having been added Warm weather shutdown and load scaling appear to be "behind the scenes magic"

  10. #140
    Automated Home Guru
    Join Date
    Sep 2018
    Location
    Scotland
    Posts
    214

    Default

    Quote Originally Posted by DBMandrake View Post
    Are you sure that's new ? Is your system TPI or OpenTherm ?

    Because on a TPI system with the default 6 cycles an hour and 1 minute on time the boiler won't fire until there is at least 10% heat demand.
    Yes, Iím using OpenTherm with my own weather compensation via OTGW and the behaviour has definitely changed with the firmware upgrade.

    The boiler was completely off, 10C demand, rather than a low 20-30C demand.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •