As others, I am also seeing the same this evening with warm weather saver enabled in that certain zones are greyed out and showing the Off icon and certain zones are showing normal working. All zones are set to use warm saver. However, I do appear to see some impact from Advanced Load Scaling being set on. Whilst a couple of the zones were showing as below temp and active, the boiler didn't fire. I left it for approx. 10 mins and still no boiler activity. One zone was 2 degrees below its set point. After playing around with Warm Weather Saver and not seeing an impact, I tried turning off Advanced Load Scaling and the boiler fired. I then tried turning Advanced Load Scaling back on (both full and partial tested) and the boiler turned off.
So two questions
1) When all zones are set to use Warm Weather Saver, what determines whether a zone shows as being "off - ie greyed out" and what determines that a zone should show as "normal" ie being active even if the zone is up to temp
2) Why does Load Scaling stop the boiler firing when some zones are in Weather Saver Mode?