Another way to look at OpenTherm low load low/off control is that Evohome has no idea what the lowest flow setpoint is. It can read the Max CH water setpoint (which is often wrong e.g. Intergas always reads 90C) but there is no minimum reading.
So if the evohome doesnt know what is the Min CH on the boiler - why is this low load invoked at all?
In my opinion it should only start demending for heat - when there is a proper heat demand from evohome - not to come on ever 10 min just for sake of it.
if this is a opentherm technology "feature" - thats surley wrong - but i suspect we may need to live with it
Do we know exactly when Low Load Control kicks in? At what % of evohome demand?
Furthermore, the boiler minimum supply temperature can be changed via boiler parameters (e.g. Intergas 10C-60C) and OT response (e.g. 0=Ignore OT demand if the setpoint for the flow temperature is below minimum, 1=Accept OT demand if the setpoint for the flow temperature is below the minimum).
In my opinion these settings are ignored when opentherm is in play. I have the boiler set to 0, with Parameter 56 set to 25C and the boiler still comes on with 25/26C - while according to settings anything below 30 should be ignored.
Am I missing anything here.
Please find attached intergas service settings for reference its in pdf