Results 1 to 5 of 5

Thread: EvoHome Beta 02.00.19.31 - Confirmed bugs

  1. #1
    Automated Home Legend
    Join Date
    Jul 2014
    Posts
    1,541

    Default EvoHome Beta 02.00.19.31 - Confirmed bugs

    Let's use this thread to report confirmed bugs.

    I'll start.

    Heating Off now stops any zone from being manually overridden. So when you turn up a zone, nothing happens. However the set point on the zone is changed and the valve pin opens. Because Heating is Off, that manually changed Setpoint is never updated back down to 5C (Off). Basically nothing happens.
    But when the HW comes on, this manually overridden zone has its valve pin still sitting Open. And gets hot!
    The easiest solution would be for the controller to reset all zones to 5C at periodic intervals. That way if a zone is manually overridden and the set point goes back to 5C, then there is some feedback in the zone to show the controller has ignored that setting. It will also stop that zone from heating up when the HW kicks in.
    Ofcourse this bug will only affect those that don't have a motorised valve on the CH loop, assuming all radiators have a HR valve on them.

  2. #2
    Automated Home Ninja
    Join Date
    Mar 2017
    Posts
    472

    Default

    HW Priority Bug - Not reheating when zone override is in place.

    HW Priority will not work when a heating zone is manually overridden - resulting in the HW not reheating until that zone override is cancelled or meets the set point. Can mean that the HW doesn't start to instantly reheat when it is required.

  3. #3
    Automated Home Legend
    Join Date
    Sep 2014
    Location
    Scotland
    Posts
    2,303

    Default

    Quote Originally Posted by mtmcgavock View Post
    HW Priority Bug - Not reheating when zone override is in place.

    HW Priority will not work when a heating zone is manually overridden - resulting in the HW not reheating until that zone override is cancelled or meets the set point. Can mean that the HW doesn't start to instantly reheat when it is required.
    Are you sure it's a manual override triggering it, and not that it's just a large heat demand from a zone ? In my case the hot water started reheating when the heat demand dropping but while the override was still active.

  4. #4
    Automated Home Ninja
    Join Date
    Mar 2017
    Posts
    472

    Default

    Quote Originally Posted by DBMandrake View Post
    Are you sure it's a manual override triggering it, and not that it's just a large heat demand from a zone ? In my case the hot water started reheating when the heat demand dropping but while the override was still active.
    It seems to be. When itís running a schedule and thereís a large demand on zones on my system it works like it should. We have a couple of zones boost at 8pm, usually when weíre drawing off large amounts of HW and it hasnít failed to recover yet - itís when thereís a manually override it doesnít function correctly - a feature I rarely use in the winter more something I use Spring/Summer.

  5. #5
    Automated Home Legend
    Join Date
    Jul 2014
    Posts
    1,541

    Default

    Evohome doesn't appear to be using the Outside temperature via an OT boiler, which has an outside sensor connected to it.