Originally posted by mtmcgavock View PostHas anyone actually considered that the issue might be with the controller rather than the CS92A?
Seeming replacing the CS92A doesn't solve the issue has anyone tried an alternate panel with a problematic CS92A.
However when I've compared the response of the controller (watching the temperature reading change during a hot water reheat and also looking at the fault logs) against my little Raspberry Pi / NanoCUL based monitoring system located near the controller, it is receiving the CS92A messages which the controller isn't, which also points the finger of blame more at the controller and less at the CS92A.
Whether the controller just has a poorer receiver or antenna than my NanoCUL or something else is at play I don't know. I like Paul's idea of extending the antenna in the Evotouch - mine is long out of warranty so its something I'd be willing to try if it's a fairly low risk procedure...
Comment
-
-
Originally posted by CT1 View PostAs distance does not appear to be a reliable predictor, could the problem be interference or crosstalk?
Comment
-
-
Originally posted by DBMandrake View PostPerhaps, but that wouldn't explain why my independent monitoring system mounted about a metre away from the controller can always hear the CS92A messages that the controller misses. Unless the controller is really slow at switching from TX to RX.
Comment
-
-
Originally posted by CT1 View PostWhat if the receiver has too wide bandwidth or suffers multi path interference? The receiver of the independent monitoring system may have better discrimination?
Comment
-
-
And the latest hot water "comms fault":
Here is what my monitoring system has received from the DHW sensor from 12pm up until 7:44pm:
Code:2020-09-16T12:03:55.595943 || DHW:CS92A | Evotouch | RQ | dhw_params | 0015020... || {'setpoint': 53.78, 'overrun': 0.0, 'differential': 4.98} 2020-09-16T12:03:55.612421 || Evotouch | DHW:CS92A | RP | dhw_params | 0015180... || {'setpoint': 54.0, 'overrun': 0.0, 'differential': 5.0} 2020-09-16T12:43:27.849412 || DHW:CS92A | <announce> | I | dhw_temp | 00134D || {'temperature': 49.41} 2020-09-16T13:33:43.178648 || DHW:CS92A | <announce> | I | dhw_temp | 0012E5 || {'temperature': 48.37} 2020-09-16T14:33:12.556016 || DHW:CS92A | <announce> | I | dhw_temp | 001281 || {'temperature': 47.37} 2020-09-16T14:36:28.581228 || DHW:CS92A | <announce> | I | dhw_temp | 001377 || {'temperature': 49.83} 2020-09-16T14:37:13.594957 || DHW:CS92A | <announce> | I | dhw_temp | 0013DF || {'temperature': 50.87} 2020-09-16T14:38:28.590636 || DHW:CS92A | <announce> | I | dhw_temp | 001447 || {'temperature': 51.91} 2020-09-16T14:40:43.602872 || DHW:CS92A | <announce> | I | dhw_temp | 0014C2 || {'temperature': 53.14} 2020-09-16T14:42:58.629919 || DHW:CS92A | <announce> | I | dhw_temp | 00152A || {'temperature': 54.18} 2020-09-16T15:42:13.016563 || DHW:CS92A | <announce> | I | dhw_temp | 001513 || {'temperature': 53.95} 2020-09-16T16:03:57.163585 || DHW:CS92A | Evotouch | RQ | dhw_params | 0015020... || {'setpoint': 53.78, 'overrun': 0.0, 'differential': 4.98} 2020-09-16T16:03:57.180186 || Evotouch | DHW:CS92A | RP | dhw_params | 0015180... || {'setpoint': 54.0, 'overrun': 0.0, 'differential': 5.0} 2020-09-16T16:18:44.255765 || DHW:CS92A | <announce> | I | dhw_temp | 0014C2 || {'temperature': 53.14} 2020-09-16T17:07:59.570439 || DHW:CS92A | <announce> | I | dhw_temp | 00145A || {'temperature': 52.1} 2020-09-16T17:57:44.899303 || DHW:CS92A | <announce> | I | dhw_temp | 0013F3 || {'temperature': 51.07} 2020-09-16T18:03:43.939994 || DHW:CS92A | <announce> | I | device_battery | 00FF01 || {'battery_level': None, 'low_battery': False} 2020-09-16T18:03:44.938888 || DHW:CS92A | <announce> | I | device_battery | 00FF01 || {'battery_level': None, 'low_battery': False} 2020-09-16T18:50:30.229182 || DHW:CS92A | <announce> | I | dhw_temp | 00138B || {'temperature': 50.03}
While preparing the screenshots for this post the fault rectified itself at 7:50pm, and the following CS92A messages have been received by my monitoring system after 7:44pm:
Code:2020-09-16T19:50:14.628982 || DHW:CS92A | <announce> | I | dhw_temp | 001327 || {'temperature': 49.03} 2020-09-16T19:54:45.653415 || DHW:CS92A | <announce> | I | dhw_temp | 001310 || {'temperature': 48.8} 2020-09-16T19:59:00.675498 || DHW:CS92A | <announce> | I | dhw_temp | 00138B || {'temperature': 50.03} 2020-09-16T20:00:00.687402 || DHW:CS92A | <announce> | I | dhw_temp | 00140A || {'temperature': 51.3} 2020-09-16T20:02:00.697454 || DHW:CS92A | <announce> | I | dhw_temp | 001485 || {'temperature': 52.53} 2020-09-16T20:03:58.724210 || DHW:CS92A | Evotouch | RQ | dhw_params | 0015020... || {'setpoint': 53.78, 'overrun': 0.0, 'differential': 4.98} 2020-09-16T20:03:58.740686 || Evotouch | DHW:CS92A | RP | dhw_params | 0015180... || {'setpoint': 54.0, 'overrun': 0.0, 'differential': 5.0} 2020-09-16T20:04:30.720909 || DHW:CS92A | <announce> | I | dhw_temp | 0014FF || {'temperature': 53.75} 2020-09-16T20:06:15.734409 || DHW:CS92A | <announce> | I | dhw_temp | 001567 || {'temperature': 54.79}
So either the Evotouch didn't receive that message at 6:50pm which was received by my monitoring system, or it reports comms faults far too quickly when it hasn't received a message in a long but normal length of time.
Perhaps someone from Honeywell can confirm what the length of time should be between the last received CS92A temperature and a comms fault being logged ? In older firmware versions I was under the impression this was 3 hours, however it seems as if this length of time has been reduced in more recent firmware versions...(which would result in more false lost comms which then quickly correct themselves) either that or it has missed receiving multiple CS92A temperature updates in a row in the prior 3 hours!Last edited by DBMandrake; 16 September 2020, 08:22 PM.
Comment
-
-
Originally posted by DBMandrake View PostPerhaps, but all these variations on a theme just result in the conclusion "poor receiver" in the Evotouch.
In my 6 years of use the one device that throws up a loss of contact is the HW sensor. Nothing else does produce a fault unless it is a battery going down.
Comment
-
-
Originally posted by G4RHL View PostBut surely if the Evotouch had a poor receiver then similar faults would be reported from HR92s etc. And not just the HW sensor. I believe your own earlier researches showed the HW sensor is weak. I changed to lithium batteries some months ago. I don’t get as many faults reported as was used to, I still get them though, just not so frequent.
In my 6 years of use the one device that throws up a loss of contact is the HW sensor. Nothing else does produce a fault unless it is a battery going down.
The Comms Failures are mainly overnight, but not always.
[My system was installed by a Honeywell approved EVO System Specialist in mid 2014.]Last edited by DerekWilliamsUK; 18 September 2020, 08:10 AM.
Comment
-
-
Originally posted by G4RHL View PostBut surely if the Evotouch had a poor receiver then similar faults would be reported from HR92s etc. And not just the HW sensor. I believe your own earlier researches showed the HW sensor is weak. I changed to lithium batteries some months ago. I don’t get as many faults reported as was used to, I still get them though, just not so frequent.
It's true that the CS92A might have a weak transmitter, but if my other device can receive it (positioned near the Evotouch) the Evotouch should be able to receive it too. In fact my device has another wall to go through as it's sitting inside the hallway cupboard near the Evotouch which is sitting on the hallway wall. So it's already at a disadvantage to the Evotouch with another wall in the way and yet it receives the messages OK.
In my 6 years of use the one device that throws up a loss of contact is the HW sensor. Nothing else does produce a fault unless it is a battery going down.
I haven't had reported comms errors with HR92's before but I have certainly had the occasional comms error with BDR91's.Last edited by DBMandrake; 18 September 2020, 09:53 AM.
Comment
-
-
The initial installation of my HW sensor was on the other side of a stud and plaster wall, less than 0.5m from the Evotouch and gave frequent comms faults. It was moved to the other side of the airing cupboard, so now about 1m from the Evotouch, and this gives less comms faults, so signal strength does not appear to be my issue. I have never had comms problems with any other devices. This does support DBMandrakes theory that it could be a timing issue with communications between the Evotouch and the HW sensor.
Edit. Battery power does not appear to be relevant as I have seen comes faults with new batteries and they do not increase as the batteries age.Last edited by CT1; 18 September 2020, 12:52 PM.
Comment
-
-
...and I now have another hot water quirk to resolve. Earlier this week my 3-way valve and control unit were replaced. My engineering skills of hitting the valve with a hammer to free it were being requested to often. After all was done, a check was made to see that it worked. The heating was switched on in the app etc. All fine. But, the next morning the HW was not heated. It is set to come on at 06:30 for an hour. The app and the Control Panel both said it was on but the boiler had not fired up. The BDR91 showed “off”. I switched it on manually. No problem. At the set time for off it went off. As it should. It fires up twice a day and it worked fine in the evening. The next two mornings the same it would not switch on at 06:30 but any other time it works fine. Not a temperature sensor issue but certainly a communication one but at the same time 3 days running. I’ll change the set time and see if that cures it!
Addendum.
I reduced the on time to 30 minutes, as that is more than enough to get the water up to 55C, resetting the start time. It worked! Not having used the Control Panel much for some time I was reminded how slow and laborious it is. Making changes is like walking in mud. We are spoilt by the touch sensitivity of our modern devices. But then the Control Panel is meant to be a modern device!Last edited by G4RHL; 19 September 2020, 09:50 AM.