Originally Posted by
DBMandrake
The valve pin positions will not be identical between multiple HR92's in the same zone in single room mode, but in my experience they'll be within about 5% of each other. Certainly not enough to explain one radiator hot and one radiator cold.
While the HR92's all have their own independent logic, when they're in a single room zone they are all receiving the same inputs - the same set point and the same measured room temperature relayed via the controller, so they tend to make the same decisions about the valve pin position.
It will be interesting to see what the three different valve pin positions are when checked.