looking at that boilers datasheet, seems to me its a storage combi?
Install manual P97 covers how the storage cylinder is controlled:
Code:
Heating the DHW loading cylinder from cold
The heating circuit pump is switched ON and the 3-
way diverter valve will be changed over, if the cylinder
temperature sensor captures a temperature lower than
the defaulted set value.
■ The cylinder loading pump is switched ON if the
boiler water temperature ≥ set cylinder temperature.
■ The burner is switched ON if the boiler water temperature ≤ set cylinder temperature, and the cylinder
loading pump is switched ON when the required
boiler water temperature is reached.
The loading cylinder is heated up to the set cylinder
temperature. Heating stops when the specified temperature has been reached at the cylinder temperature
sensor.
Reheating when DHW is drawn off
When DHW is drawn off, cold water enters the lower
section of the loading cylinder.
The heating circuit pump is switched ON and the 3-
way diverter valve is changed over, if the cylinder temperature sensor captures a temperature lower than the
defaulted set value.
■ The cylinder loading pump is switched ON if the
boiler water temperature ≥ set cylinder temperature.
■ The burner is switched ON if the boiler water temperature ≤ set cylinder temperature, and the cylinder
loading pump is switched ON when the required
boiler water temperature is reached.
which makes perfect sense - the controls for these are internal to the boiler. looking at the electricals, in the manual on Page 99
S - terminal block X5 terminals 3 and 4 - cylinder temp sensor
O - terminal block X9 terminals 1 through 6 - diverter valve motor controls
so theoretically I suspect you could tap into those terminals and put in external switching / control of your own making . However, warranty would be likely be dubious in this situation - I wouldn't do it.
looks like the opentherm controller for this device is for heating control only.
what hot water kit do you mean? I have one for my heat-only viessman but I don't see how that applies to a storage combi?