Viessmann was one of my options when looking for a new boiler three months ago Viessmann recommended an approved installer who is about 10 minutes away from me and said he could quote but never did and ignored me. I went for Intergas which had been my main choice. I cannot go as low as 3.2kw max for CH, which is what the new Viessmann is noted for, but I can drop to 6.4kW and set it at that some weeks back. No problems at all. Also have dropped the flow temperature to 65C. It works absolutely fine. Out of interest did your installer know about properly setting it, flow and condensing temperatures and power settings? My experience has been that over 95% have little or no knowledge of such (even so called approved installers) and leave boilers installed as they come with default settings. In your case 80C I assume and maximum kW for CH.
With the Opentherm connection with the Intergas it just happens and works once the bridge is connected. ECO mode I removed. Could not see the need for it and it only burns more gas than is necessary. It might take slightly longer for hot water to reach the tap but the time is marginal and we don’t have the boiler firing up every so often just to keep DHW in readiness.