Summary status on Evohome missing BDR
Hi - just a quick piece of help needed.
I have self installed. Followed instructions. Y plan system. 2xBDR's. One bound to hot water (also with hot water thermostat). One bound to heat (from 3 port valve). 12(+1) HR92's bound as separate zones ( one room has 2 rads)
SO... on in the system summary I see, Hot Water and 12 zones bound ( 13 lines altogether). I do not see the heat BDR bound or named although it seems to work. Is this correct???
Thanks in advance.
-
7th October 2021, 05:37 PM
#2
Automated Home Guru
You have an identical setup to me, and yes what you describe is normal.
-
8th October 2021, 12:38 PM
#3
Automated Home Guru
Agree. In my mind the system summary is showing demand for each zone and the dhw. The heat relay does not have it's own demand.
-