Evohome, DHW priority and x-plan

Collapse
X
 
  • Filter
  • Time
  • Show
Clear All
new posts
  • lloyd
    Automated Home Guru
    • Oct 2020
    • 160

    Evohome, DHW priority and x-plan

    I'm looking at replacing my boiler, probably with Intergas. I already have EvoHome complete with DHW control.

    The question I have is around DHW priority. There are a number of articles that suggest that x-plan is the way to go, so you can have hotter water heating the cylinder than heats the rads.

    However, Evohome has a DHW priority function, and I was wondering how that works, especially when utilised in conjunction with OpenTherm? Does anyone have any knowledge or experience of this?

    PS Any recommendations for Intergas installers in the Bedford area appreciated.

    Thanks
  • bruce_miranda
    Automated Home Legend
    • Jul 2014
    • 2307

    #2
    In order to use HW priority, you will need BDR91 controlling the HW and CH loops, in addition to your OTB that fires the boiler.

    Comment

    • lloyd
      Automated Home Guru
      • Oct 2020
      • 160

      #3
      Is that true with x-plan? I thought in that case the CH loop opened when the DHW loop was closed. ie just one BDR91 on the DHW loop.

      Comment

      • bruce_miranda
        Automated Home Legend
        • Jul 2014
        • 2307

        #4
        The Evohome now allows you to implement DHWP regardless of the way the system is piped.
        You could always implement DHWP with an X plan with a single relay and using a Normally Open Valve.

        Comment

        • lloyd
          Automated Home Guru
          • Oct 2020
          • 160

          #5
          Thanks. I guess that was what I was trying to determine. To make sure I have this correct. DHWP is a new feature in the latest firmware. Before that existed x-plan would have been the way to do it, but with the latest firmware DHWP can be achieved with y-plan or s-plan.

          Any advantage with either method?

          Comment

          • bruce_miranda
            Automated Home Legend
            • Jul 2014
            • 2307

            #6
            Not that I can think of, the software now just gives existing installations the option. What we fought for though was the forced DHWP setting that couldn't be turned off. Thank goodness Resideo listening and made that switchable

            Comment

            • mtmcgavock
              Automated Home Legend
              • Mar 2017
              • 507

              #7
              Doesn't work well with Opentherm. I ended up changing my NC Motorised valve to a NO one as per the old system before the Firmware update.

              The issue is Opentherm fires the boiler for low flow temps, while the BDR91 keeps the CH motorised valve closed because of the TPI cycling issues. So defeats the object. Found on many occasions the boiler firing and CH valve closed, hence the change to a NO.

              Comment

              • bruce_miranda
                Automated Home Legend
                • Jul 2014
                • 2307

                #8
                I absolutely hate that TPI is built into the firmware of the BDR91. It should have been overrideable. Worse still the relay settings available in the Controller then go and apply to all Relays in the system.
                This is one reason why I moved away from using a BDR91 for my UFH.

                Comment

                • lloyd
                  Automated Home Guru
                  • Oct 2020
                  • 160

                  #9
                  So the TPI issue is probably sufficient to send me down the x-plan route. Out of interest, does the evohome opentherm implementation allow different flow temperatures for DHW and CH? (I believe this is achieved by the wiring with x-plan and intergas, just interested from a theoretical perspective)

                  Comment

                  • bruce_miranda
                    Automated Home Legend
                    • Jul 2014
                    • 2307

                    #10
                    Originally posted by lloyd View Post
                    So the TPI issue is probably sufficient to send me down the x-plan route. Out of interest, does the evohome opentherm implementation allow different flow temperatures for DHW and CH? (I believe this is achieved by the wiring with x-plan and intergas, just interested from a theoretical perspective)
                    Nope,another missed opportunity, even though the OTB is able to distinguish between CH and HW workloads, it doesn't do much with it. Except when heating HW it goes from 10C to 90C demand only. Whereas with CH, it can do several stops between 10C and 90C. What you really need is a way for the boiler to raise the max flow clamp ceiling when doing HW. Intergas allows that. I have been able to do that on my Vaillant too. I previously did it programmatically using Domoticz and an eBus interface. Now I use the Vaillant wiring Centre and the microswitch inside the HW zone valve.

                    Comment

                    • lloyd
                      Automated Home Guru
                      • Oct 2020
                      • 160

                      #11
                      On the Intergas x-plan wiring diagram, there is a cylinder ntc sensor. Does anyone know what part this plays when there is also a cylinder sensor for Evohome?

                      Comment

                      • bruce_miranda
                        Automated Home Legend
                        • Jul 2014
                        • 2307

                        #12
                        My guess is based on the Vaillant but it will be similar. The Intergas Cylinder NTC will tell the boiler what the temperature of the water in the Cylinder is. There must be some HW settings on the boiler. But when you use Evohome, the boiler doesn't need to know what the temperature of the water is, Evohome does. So use only the Evohome NTC sensor. You still need to keep the Cylinder's main cut out sensor in place as a fail safe. So check if the Intergas NTC is not actually that. I can't see it being that though.

                        Comment

                        • mtmcgavock
                          Automated Home Legend
                          • Mar 2017
                          • 507

                          #13
                          I have a Main and have an X plan.

                          Evohome does differentiate between HW & CH. When my Opentherm requests HW reheat, it demands an 80oc flow temp. On CH it modulates to what it likes, which is usually 30oc. At which point I get a bit of cycling, however I did realise this would happen and it was a trade off. However it works fine and really lowered my gas consumption. I just use the Evohome NTC sensor.

                          Comment

                          • bruce_miranda
                            Automated Home Legend
                            • Jul 2014
                            • 2307

                            #14
                            Originally posted by mtmcgavock View Post
                            I have a Main and have an X plan.

                            Evohome does differentiate between HW & CH. When my Opentherm requests HW reheat, it demands an 80oc flow temp. On CH it modulates to what it likes, which is usually 30oc. At which point I get a bit of cycling, however I did realise this would happen and it was a trade off. However it works fine and really lowered my gas consumption. I just use the Evohome NTC sensor.
                            Evohome will use a 90C flow temp on 100% heat demand, whether that demand is from HW or CH. Hence why I say it doesn't differentiate between HW and CH. HW will only ever go from 0% to 100% heat demand. CH on the other day can have a Heat Demand between 0% and 100% and that is when you will see the lower Flow temperatures.
                            What OT and Evohome could have done is used the fact that it knows if the demand is from HW or CH and used a different desired max flow temperature.

                            Comment