help to wire programmable room thermostat
Help needed
I have just bought a Honeywell cm67 programmable thermostat to replace an ancient Sunline Proscon and give me more control, problem is the Sunline has four wires Red (L), Blue(N) and Yellow + earth and the Honeywell has only two terminals, i have fitted the L & N as per the diagram but this just blows the fuse, can anyone help by telling me what i need to do with it to stop it blowing fuse's??
-
29th January 2006, 08:06 PM
#2
Automated Home Lurker
Re: help to wire programmable room thermostat
The CM67 is battery powered it is only used to switch the boiler, I would be pretty certain that you only connect the red & the yellow.
Red = Live
Yellow = Switched live to boiler
-
30th January 2006, 04:15 PM
#3
Automated Home Lurker
Re: help to wire programmable room thermostat
Thanks for your help on this one, you were spot on , it's working fine.
Firts time that i have used this site!
Thanks for the advice.