    Hi Michael D, re. your post from 5th December - sorry, I have been on holiday for a week so haven't had a look on this forum. Just in case you didn't find an answer to your questions already:

    1. Each radiator does *not* require its own thermostat. Each room/zone needs a thermostat, and each thermostat can control up to 8 radiators (through automatic wireless control of the rad. valves). The tech. spec. states that the wireless transmission range between thermostat and rad. valves is 100 metres free field. Even allowing for signal attenuation through walls etc, there should be no problem locating the thermostat in a separate room from the rad. valves/radiators it is controlling, if that's what you need.

    2. I'm afraid I don't know the answer to your question about the WebConnect software - I think you should email customer support at HouseTech UK for some help on that one.

    Hope that helps you - feel free to ask anything else if you think I can help.

    Comment

    • BrianH
      Automated Home Lurker
      • Dec 2008
      • 1

      #17
      Hi all,

      I have been reading this thread with interest, I have a qusetion I wonder if anyone can answer.
      My system at home has a programmer/timer which controls both heating and hot water from a gas condensing boiler. I set the heating to come on at 0700 and go off at 2300. I also have a thermostat in my hallway which is conected elcetrically to the programmer/timer I think, and I then select the temp I want in my hallway. There are TRV's on all radiators.
      If I fit the Househeat system with radiator valves and thermostats in each room, and fit the Housemaster control panel to control each thermostat, does anyone know if the housemaster control panel will replace the function of my hallway thermostat and open and close the electrical circuit to my programmer to tell it to switch on and off when the househeat system demands it?, therefore I can leave my heating setting in the programmer to always on.

      Comment

      • mikep
        Automated Home Lurker
        • Jan 2009
        • 1

        #18
        Hi Ian,
        Thanks for the info - a couple of Qs. I am looking seriously at the HouseHeat products and would be interested to know what brand of TRVs you have and also whether you used the FHZ1000? I want to run around 6 zones and want to avoid the need for multiple master units for ease of use.
        Regards
        Mike...

        Comment

        • IanJ
          Automated Home Lurker
          • Oct 2008
          • 6

          #19
          Hi Mike,

          I have Siemens thermostatic radiator valves - the HouseHeat valve motors fitted directly on to the thread of the valves with no need for any adaptor, although I am aware that HouseTech can supply adaptors for other valves if you need them, and adaptors for Danfoss valves came bundled with the product. I have a friend who has also subsequently bought and fitted a HouseHeat system after seeing mine - he has TRVs from Wickes, and again, he was able to fit the HouseHeat valve motors directly on to the valve thread with no adaptors required. I believe that if you have TRVs with a 'standard' M30 x 1.5 mm thread you will not need to use an adaptor to fit the HouseHeat product on to the TRV.

          I did not go for the FHZ 1000 HouseMaster product, so can't offer any advice on that, although my understanding is the same as yours, that it acts as a master controller for programming and displaying data from all the zone thermostats dotted around your building. I just bought the basic HouseHeat system with the wireless zone thermostats and the wireless valve motors.

          I have, however, recently installed the HouseHeat boiler-control product (BoilerConnect) to enhance the system further, which also seems to work faultlessly.

          Comment

          • andy_p
            Automated Home Jr Member
            • Jan 2009
            • 13

            #20
            Alternative software

            Hi - first post

            Any chance they'll let people buy just the valve motors and the usb interface, and use our own software? I've been running my own pc-based system for 5 years now, but never found a convenient way to control individual radiator valves. I'm sure it's possible to use their web server box and talk to that, but doing that seems a bit over-engineered and expensive.

            I've mailed the company direct; guess I need to wait until monday to see what their reply is.

            Comment

            • Kevin
              Moderator
              • Jan 2004
              • 558

              #21
              I'd be most interested in the reply you get. Should they be amenable to some alternate form of software integration - I'd be interested in buying a fairly large system and adding xAP support which would allow integration of their system inside most of the current HA software applications (HomeSeer, CharmedQuark, HouseBot, MisterHouse, xLobby, xAP Floorplan, Girder, Premise etc).

              K

              Comment

              • Kevin
                Moderator
                • Jan 2004
                • 558

                #22
                Some thoughts.. .. not sure if anyone has any answers - overall for the price it looks to have lots of possibilities though...

                The radio system seems 1-way to most modules - namely to the valves and the boiler controller, so no confirmation that things are being received OK

                Following on from the above it would seem the thermostat cannot know/take account of flow temperature when calculating how much to open a valve. If your boiler automatically modulates the flow temp (as mine does) this could be an issue.

                I wonder how much the thermostat learns about an individual rooms thermal behaviour or if it's just a slow feedback loop and not modified based on previous behaviour.

                No HotWater integration

                I personally would have preferred six programmable temp changes per day and to choose between three rather than two setpoint temperatures (you can't select 'off' ie frost on a timed basis)

                No separate sensors for remote mounting of a thermostat

                No external temp sensor to do any weather compensation

                No optimum start inbuilt

                No mention of inline valves for pipes to rads although I'm sure they exist

                Not sure quite what is configurable via the web interface, eg if you can reprogram the setpoint change times etc rather than just overide current temp.

                Shame they haven't updated the display interface for English.

                No detail on the USB interface - actually there are several variants available inc an Ethernet (WiFi) one.

                Other HA bits on German site (and eQ-3) look interesting although the controller is expensive. The whole 'bidCoS' RF system seems to be based on a very low cost Chipcom cc1000 TI part.
                Nice brochure here


                K
                Last edited by Kevin; 12 January 2009, 05:40 PM.

                Comment

                • andy_p
                  Automated Home Jr Member
                  • Jan 2009
                  • 13

                  #23
                  got an answer, but it's not the one I was hoping for:

                  I'm afraid it is not possible to operate the system using your own software - it only works as an integrated package using all the HouseHeat components listed on the web.
                  So... I'm thinking about using z-wave instead:
                  The rad valves might be almost double the price, but at least it's an open standard, I won't have to buy anything I'm not going to use, and I'll definitely be able to integrate it into my existing system and make it do what I want.

                  Comment

                  • Kevin
                    Moderator
                    • Jan 2004
                    • 558

                    #24
                    I too have looked at Danfoss - not ruled them out yet but it's not quite right for what I want.

                    With the Danfoss rad valves they can only be manually set to a temperature and then controlled via Z-Wave with an on/setback command. The setback temp is fixed at a few degrees below the main setpoint , 3.5 degrees or something from memory.

                    Nor can you IIUC read the current room temperature or valve postion (% open) back from the valve. Z-Wave does have the advantage of confirmed RF receipt though.

                    For me this is a big problem as I would like the setback to be much lower than that fixed value, and also to be able to select an off (well frost protected) mode too. Ideally I just want to send a setpoint temperature to the valve and let it get on with it, providing a % open value feedback would be a bonus.

                    K

                    Comment

                    • Kevin
                      Moderator
                      • Jan 2004
                      • 558

                      #25
                      Not sure what the software is that comes with the USB interface for HomeHeat. It says it's single zone restricted but can easily be expanded. If the software is 'HomePuter' or if the HomePuter Studio software is useable with the heating system then the German site shows a DLL as being available for 69€ . I am not sure of the interoperability of the heating system with the other HA items/system.

                      K


                      PS Here's the Google translation...


                      The DLL provides functions that allow objects and variables homeputer the studio version when queried active execution and can be changed. It is possible regardless of the hardware with their own programs into the controller to intervene.
                      How DLL's in a programming language used is the language-dependent. Instructions for use of the DLL and the functions of the DLL are in the associated PDF file.
                      The download file contains examples in Delphi 2006 and Borland C + +.
                      The use of a DLL requires knowledge!
                      contronics can not provide support regarding the involvement of the DLL in the various programming languages or other support concerning the programming of the individual application.
                      The DLL 10 days can be used free of charge, after 10 days must be included with the program FreigabeDLL2.exe a release code, to the perpetual use of the DLL release.
                      The license fee associated with ordering the release of code is due is 69,00 Euro.

                      Comment

                      • andy_p
                        Automated Home Jr Member
                        • Jan 2009
                        • 13

                        #26
                        danfoss valves

                        that's a shame about the danfoss valves; they don't sound quite so good now.

                        The other method I was considering was to use thermoelectric actuators for the rad valves, but they'd need to be permanently wired as they take too much power for batteries. It might be possible to use a mains (e.g. x10) module to drive them though.

                        You could probably get separate temperature sensors and let your controller use that to decide when to turn the heating on or off. I'm currently doing that, using an x10 module to spoof the boiler thermostat, and it works quite well, but I obviously can't control which room gets the heat.

                        Comment

                        • andy_p
                          Automated Home Jr Member
                          • Jan 2009
                          • 13

                          #27
                          HomePuter

                          I've looked at the example code and documentation they supply - the API mainly revolves around the following functions:

                          homeputer_SetObjValName(char*, char*)
                          homeputer_GetObjValName(char*, char*)

                          gets or sets the current value of the named object, or object variable (using "name.variable" syntax).

                          Of course the usefulness of that would depend on what values they make available...

                          homeputer_SetWindowHandle(DWORD)
                          It will send a windows message to the registered window handle every time an object in the Studio software changes. wParam is the index of the object being changed.

                          It rules it out for me though; I want my current system to be able to run as a windows service without being logged in, so it won't be able to run another gui program either.

                          Bottom line for me is that even if the uk distributor was able to help, I think I'd be better off using something else.

                          Comment

                          • Kevin
                            Moderator
                            • Jan 2004
                            • 558

                            #28
                            Originally posted by andy_p View Post
                            Bottom line for me is that even if the uk distributor was able to help, I think I'd be better off using something else.
                            Well three telephone calls to UK number (all diverted to a mostly German speaking answer phone) - no return call and no reply to my email suggest that they're not too much help at all :-( - enquiry was sales oriented too....

                            Comment

                            • Hoo
                              Automated Home Lurker
                              • Jan 2009
                              • 2

                              #29
                              Hello Everyone.
                              I've been watching this thread in the hope that someone would have some luck with controlling the Househeat devices.
                              I can't say that I had much hope from looking at their site, and the response Andy_P and Kevin received confirmed this.
                              Still, they look like a very good system for the price, I just have to find a way of hacking the protocol. I get the impression that this has been done from the links that were posted earlier, but since it's all in German I can't be sure! Looking at the stuff on the German site it looks like it would be possible to send commands to the devices using the PC Interface and listening in, either by monitoring the virtual serial port or the radio transmission, and from that reverse-engineer the protocol. I get the impression that the radio link is a standard protocol, so tranceivers should be available.
                              Does anyone have enough German to confirm this?

                              Comment

                              • andy_p
                                Automated Home Jr Member
                                • Jan 2009
                                • 13

                                #30
                                Originally posted by Hoo View Post
                                Does anyone have enough German to confirm this?
                                Google does
                                That's how I got the docs out of the german pdf.
                                It's also why I stopped after only 3 functions!

                                This might be a good starting point on contronics.de

                                This wiki attempts to understand FHZ1000PC, BidCos and HomeMatic etc. (I've left it in google translate because some of the linked pages are in german, even if that page in in english).

                                Let us know how you get on; the hardware would be a very attractive price, if only the software wasn't so closed.